Is it acceptable to use a spare core in a 4 core armoured cable to carry 12volts DC when other cores in the same cable are carrying AC mains?
Discuss AC mains and low voltage DC in same cable? in the UK Electrical Forum area at ElectriciansForums.net
How will you get induced voltage on the dc circuit if the cores are insulated to the highest voltage present i.e. 230volts?You will also have to take into account harmonic effects from the AC and quite possibly induced voltage on the DC circuit.
How will you get induced voltage on the dc circuit if the cores are insulated to the highest voltage present i.e. 230volts?
Band 1 (ELV) and Band 11 (LV) circuits can be contained in the same cable where each conductor of a multicore cable is insulated to the highest voltage present i.e the Band 11 voltageInsulation rating does not effect induction, however as the OP is discussing a multicore cable then to comply like you and others have put it has to have a earthed screening which will block any chance of an induced current between the 2 categories as we must assume AC mains means 230/400 volt ac against his 12v DC, as for harmonics, if you suspect this as an issue then the wiring and preventative measures in total needs careful design.
Band 1 (ELV) and Band 11 (LV) circuits can be contained in the same cable where each conductor of a multicore cable is insulated to the highest voltage present i.e the Band 11 voltage
As stated in option 2 given in bs 7671
Is the ELV Ethernet insulation rated the same as 230 v cables?Is it permissible to run ELV Ethernet over LV 230V ac cables?
yep agreed I've re read it over and it does say system , I even wrote the dam thing on the thread.As I interpret it that is for the same wiring system, they have made a specific regulation exemption No' 6 for multicore cable as that does not fall under the term same wiring system due to the fact its a cable and not multiple cables or cores in a wiring system.
See further replies in the thread pal.This is interesting as I come across this a lot and never use the cable for ELV as worry about interference.......so you reckon there can't be an induced voltage due to the insulation Ian? Surely that can't be the case as you can get induced voltage from LV to LV? Or am I getting it wrong? Would be handy to be able to use the same cable for ELV and LV.
I would assume so, as the conductors used for the Ethernet are the ones already being used for the 230V.Is the ELV Ethernet insulation rated the same as 230 v cables?
Then no