Discuss Accenta G4 external siren only sounds on bell test in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Reaction score
0
Hi, I have an Accenta G4 8SP399A with a single LCD keypad.

Everything seems to be working correctly other than the external bell doesn't sound when the alarm is triggered, the strobe lights do light up though.

If I do a bell test via the engineers menu the external bell does sound.

Would anyone have an idea what might be causing this?

Thanks in advance.

Mark
 
Is the applied negative working when the panel is in alarm mode? Maybe the circuit board isn'g sending the signal, connect both bell and strobe terminals to whatever the strobe is connected to in the panel and see if that works
 

Reply to Accenta G4 external siren only sounds on bell test in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

Hi All, We have had an Acenta G4 alarm fitted for 5 years. It has been fine until recently, however the keypad now appears to have failed...
Replies
2
Views
2K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K
I have a Aritech CS450 which has been working fine for a number of years. All of a sudden the "Trouble" light came on the keypad. I checked the...
Replies
12
Views
4K
Hi All Just installed a Honeywell Accenta G4 and everything works perfectly. I have a remote keypad upstairs on the landing. I have Program 2...
Replies
13
Views
7K
Hi all, just powered up a G4 Accenta and I'm having trouble with the remote keypad. The red and green indicator led's are lighting up,but thats...
Replies
9
Views
9K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock