Looking closely it doesn't look like a wago. This one's got curved edges.

They look like the Ideal In-Sure® Model 33, www.idealindustries.co.uk/product/12/204/67899/.html which are 32 Amp rated, so one can assume there was a problem with the wire not being fully inserted or something?

The Ideal 2, 3 & 4 way ones are 32 Amp, which is why I use them, as they can be used for ring main cables.
 
They look like the Ideal In-Sure® Model 33, www.idealindustries.co.uk/product/12/204/67899/.html which are 32 Amp rated, so one can assume there was a problem with the wire not being fully inserted or something?

The Ideal 2, 3 & 4 way ones are 32 Amp, which is why I use them, as they can be used for ring main cables.

So can a 20A as generally a ring final circuit is designed around the assumption of a load at 20A at the furthest point of the circuit and the remainder to the rating of the over current protective device evenly distributed around the ring final circuit.
 
So can a 20A as generally a ring final circuit is designed around the assumption of a load at 20A at the furthest point of the circuit and the remainder to the rating of the over current protective device evenly distributed around the ring final circuit.
Surely if the ring provides power to the kitchen & utility, then someone further down the line does something wrong to break the ring, which is not picked up until the next EICR if they bother to have it done, then those poor little 20 Amp connectors will be the weakest link & will fail before the fuse or circuit breaker disconnects?
 
Surely if the ring provides power to the kitchen & utility, then someone further down the line does something wrong to break the ring, which is not picked up until the next EICR if they bother to have it done, then those poor little 20 Amp connectors will be the weakest link & will fail before the fuse or circuit breaker disconnects?
same could apply to a 32A wago/ideal/hellerman push in connector.
 

Reply to Accessible or inaccessible? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I carry out PAT testing on landlord appliances for letting agents in rented accommodation. Occasionally some of the items I cannot access...
Replies
5
Views
703
Hello all, I need to have an electric car charger installed but at the moment I'm puzzled about what my options are. My garage is at the back of...
Replies
4
Views
648
  • Question
Hi All. I need to extend the cables for a 3 plate ceiling rose/pendant on ground floor ceiling by 450mm. Can I fix the ceiling rose/pendant to...
Replies
5
Views
343
I was asked to see why a set of sockets weren’t working in the house (which appear to be a ring circuit based on breakers) There was no power on...
Replies
27
Views
1K
What is best practice when unable to access a plug on a class 1 appliance. Specifically a washing machine in this instance. There is also no...
Replies
3
Views
714

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock