R

Richard3009

Split load main CU in the house, all the ways have RCD protection, we now supply the garage/shed from one of those ways and install a neat little 2 way submain in the garage, is there any real benefit in having an RCD in the submain, because the only way to descrim is by fitting an S type in the main CU, one option would be to henley block main tails in the house and power the garage via an MCB with no RCD using SWA, and then protect in the garage with its own RCD, also creating the chance of getting the freezer off RCD protection with a bit of steel conduit. Any thoughts.
 
SWA - are fine rcd in garage... as for the fridge or freezer then rcbo' it regardless of the install nature a socket outlet requires rcd protection.

If this is your house you could use a get out clause of a responsible persons reg' but really not what its designed for so go with a separate rcbo on the freezer.

If it trips that then you have a faulty freezer or circuit end of ad need to ensure your family stay fully protected
 
split tails as you say. in garage fit a 3 way sub. MCBs for freezer and lights. RCBO for general sockets. ( assuming surface wiring in garage)
 
SWA - are fine rcd in garage... as for the fridge or freezer then rcbo' it regardless of the install nature a socket outlet requires rcd protection.

If this is your house you could use a get out clause of a responsible persons reg' but really not what its designed for so go with a separate rcbo on the freezer.



If it trips that then you have a faulty freezer or circuit end of ad need to ensure your family stay fully protected

Can't you use the exception in
Reg 411.3.3 (b) A specific labelled or otherwise suitably identified socket outlet provided for connection of a particular item of equipment.

But you do have a good point if there is a fault on the freezer it will trip the RCBO out, better loosing a load of food then a life
 
split tails as you say. in garage fit a 3 way sub. MCBs for freezer and lights. RCBO for general sockets. ( assuming surface wiring in garage)

With regards to 411.3.3 (b) - giving exception of RCD cover for labelled ad outlets for use of a specific item .... I might consider it for a Kidney Dialysis machine in domestic where a unwanted trip could be costly but for the extra safety a rcbo will give the family I don't think the OP needs to omit rcd protection its highly unlikely to trip unless fridge/freezer is actually faulty.

Ps My freezer has been on a rcbo several yrs and never tripped although the rcd covering sockets has --- I do like to experiment with control gear ;)
 
Last edited:
With regards to 411.3.3 (b) - giving exception of RCD cover for labelled ad outlets for use of a specific item .... I might consider it for a Kidney Dialysis machine where a unwanted trip could be costly but for the extra safety a rcbo will give the family I don't think the OP needs to omit rcd protection its highly unlikely to trip unless fridge/freezer is actually faulty.

A fair point, back to my point on RCDs in series, best avoided difficult to descriminate.
 
A fair point, back to my point on RCDs in series, best avoided difficult to descriminate.

Yes your garage prone to damp, water ingress normally more so than house electrics .. don't do rcd in series you asking for nuisance tripping of half the house possibly ...Swa as i suggested earlier or other mechanically protected option.
 
With regards to 411.3.3 (b) - giving exception of RCD cover for labelled ad outlets for use of a specific item .... I might consider it for a Kidney Dialysis machine where a unwanted trip could be costly but for the extra safety a rcbo will give the family I don't think the OP needs to omit rcd protection its highly unlikely to trip unless fridge/freezer is actually faulty.

Good point , but the reg doesn't state specialist equipment just a particular item, this reg could easily be abused and could put lives a risk, although I not yet herd about any one being electrocuted by a fridge yet
 
A fair point, back to my point on RCDs in series, best avoided difficult to descriminate.

Not sure on size and configuration of the The CU, if there room you could put a separate RCBO in the board fed from the main switch ,But as Darkwood says the best way is MCB and feed Garage with SWA
 
Consumer death rates are nationally very low given the size of our population and yes we functioned ok for several decades without them, now their here they often are preached as the magic bullet of safety but i reality they just reduce the risk but at the end of the day what £20 extra - a good return for the safety that it provides in my mind - and most freezers will hold temp for 4hrs plus if power loss anyway.
 
With the new amendments due and I believe a tightening up on circuits exempt from RCD protection my thought is we shouldn't really be looking for ways now to omit the need for an RCD in domestic environment. They do provide extra level of safety so should be implemented especially on circuits with items that usually supplied with a plug top - trying to step around this to reduce costs or try eliminate what is ill perceived as nuisance tripping (Ive fitted loads of dedicated circuits to rcbo's and never had issues with nuisance tripping)..... its rare on dedicated circuits so shouldn't be an argument for a case of no earth leakage protection nowadays.
 

Reply to Achieving descrimination with RCD protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
679
Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
465
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
855
I have found out that my electricity supply in my external garage is wrongly connected to my neighbours electricity unit in their house and their...
Replies
19
Views
3K
Hi all Now being upfront I am not a sparks. I am about to have some work done by a friend (certified) and as he is doing me a favour I want to as...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock