Depends on:Hi,
Can anyone give me some advice on how I add a mains plug to the following circuit,
The FCU is connected to a home alarm system and I would like to add a normal plug socket, any advice would be greatly appreciated
Thanks
View attachment 39684
View attachment 39685
View attachment 39686
What size his the cable 1.0mm2 1.5mm2 or 2.5mm2?
You can if you go through a fused spur! Appendix 15 BS 76571Firstly i would get that supply to the alarm sorted out it looks
Like the supply cable, is run with the alarm cables and very close to pipe work, also as morduch says if thats on a 32 amp fuse you can not spur of it with a socket as you only can have one point spured off the ring circuit , that if is a ring ,
Firstly i would get that supply to the alarm sorted out it looks
Like the supply cable, is run with the alarm cables and very close to pipe work, also as morduch says if thats on a 32 amp fuse you can not spur of it with a socket as you only can have one point spured off the ring circuit , that if is a ring ,
Get him to change that spur to an unswitched one while he's at it.Thanks guys appreciate the advice I think I need to get an electrician in and maybe somehow get another supply in the area!
because it should be unswitched for an alarm supply.Delete.
Yeah realised my error thought it was for a boilerbecause it should be unswitched for an alarm supply.