OK...
You must have a permanent live at the switch.
Just connect a piece of twin&earth from the switch. You'll need perm live and earth.
Poke it to the fan inlet hole. Then grab your existing fan cable. You then have all that you need for the over-run add-on unit. You'll have to decide where (accessible) that you can locate this.

That should sort the over-run issue. The you have the issue of the fan extract pipe, oh yes and what you do when the fan dies.
 
Update on this.

Added in a FCU before the bathroom switch, back up the wall and mounted a manrose timer unit, 3 core and earth from switch, and t&e from unit to fan.
Lights are on a different t&e from switch.

Works fine, or so I thought. Lights and fan come on with switch, lights go off with switch, fan runs on for set time....

Except. The inlet grill of the fan has a 12v led lamp built into the centre of it. Wired correctly on the lighting side. With the lights on, it works ok. With the switch off, and whether the fan is running or not, this lamp flashes once about every 5 seconds.

Reason? I think it’s getting a back feed from the timer unit back down the switch wire which is making the light flash.
It may be that the transformer for the12v isn’t right. Meaning it’s designed for a halogen lamp rather than LED.
I’ll change that first to a LED driver.
If that doesn’t work, double pole switch in place of light switch. Using the second pole to isolate the timer sw from the lights.


Not asking a question. Just thinking out loud.
 
It may be that the transformer for the12v isn’t right. Meaning it’s designed for a halogen lamp rather than LED.
That will be the reason. Most of the halogen "transformers" don't work unless they have around 20VA on the output, and your LED will be way less than that.

May just be easier to pop a holgen lamp back in there.
 
It's been working with an LED in it up til now. Its just adding the timer that has caused a problem.
I'm not actually sure the transformer that's there is original.

Tomorrows job is to wire the kitchen best way I can with limited wall space and more appliances than kitchen units
 
Yes. I’ve only got a sw and n. What I need is the fan to be powered from a timer unit which is triggered by a light switch, not from the light switch itself.
I realise I need a 3 core to operate the timer... but that is straightforward from the switch as there’s a live, sw an neutral there.

Swapping out the fan for a timer version or 12v is impossible without taking down the ceiling.

It may be I could use a humidistat?
or a PIR unit.
 

Reply to Adding a run on timer to an existing fan in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Hi all, Got an awkward bathroom fan installation in a downstairs flat, concrete ceilings and (some) walls. Bathroom is already fully tiled and...
Replies
1
Views
600
Hi All, Bit of a tricky number. I have recently installed lights / fans /toothbrush chargers and shaver sockets to a bathroom and En-suite. The...
Replies
6
Views
1K
Hi, The house I've moved in to doesn't have an extractor in the main bathroom so I'm looking at placing an inline extractor in the attic directly...
Replies
5
Views
3K
Hi i am looking for some advise regarding a bathroom extractor fan currently fitted to my new bathroom refurbishment. Problem i have is a...
Replies
2
Views
1K
Got a job coming soon that’s going to be a nightmare, but in the meantime there’s a few odd jobs to do. One of them is to replace a timed fan in a...
Replies
42
Views
4K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock