Discuss Addng cpc to two core lighting circuit in the Industrial Electricians' Talk area at ElectriciansForums.net

L

LlandrilloSpark

Fellas is it permissible to run a single 2.5mm in a loft or do really need double insulated?, there has been an attempt to add an earth to the circuit before but they missed the switches out and some fittings are 32Ohm R1+R2, it's in a bungalow so should be easy
 
I think it has to be over 6mm if you're installing it without mechanical protection.
Could you just rip it out and do it all in bog standard T&E? Might be easier, neater, cheaper etc.
 
I had thought of a circuit rewire but only 4 lamps are effected and the switch back boxes have plastic lugs so they don't even technically need earthing if the patress screw doesn't touch the back box, and all the switched are PVC, cheers for the 6mm advice
 
It has to be 4mm min if it hasn't got mechanical protection (543.1.1) but what's usually the hardest part adding one is that it has to be incorporated in the same wiring system or in the immediate proximity of the live conductors (543.6.1) which means dropping one down to switches etc so it's probably easier to just rewire.
 
Think even the back boxes have to be earthed even if not technically required now to allow for somebody putting in metal casing switches in the future .
 

Reply to Addng cpc to two core lighting circuit in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
412
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, I have an unusual issue with a recent rewire I have just completed which I hope you guys can assist with. For background, this is a...
Replies
19
Views
2K
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K
When I checked out this job I had a false sense of security from a recent competent looking EICR and two new CU's that looked to be fitted to a...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock