Markie Mark

Hi,

I need to rewire our Sky Box and CCTV System and I wish to use the existing conduit which currently houses five 240 volt main lines running for about 30 feet.

I'll be hoping to consolidate in this same conduit Ethernet cabling x 2, RJ-11 x 1, AV Cable x 2 and Sky Coax x 2. I am concerned about electromagnetic interference and therefore wondered if anybody has a similar setup running smoothly?

Many warm regards.
 
Re: Advice needed on consolidating av and coax cabling alongside five 240 volt main l

Welcome to the forum Markie Mark.

I've moved this thread to the Sky TV forum for you.
 
Re: Advice needed on consolidating av and coax cabling alongside five 240 volt main l

Power and signal/data cable should not be grouped together in the same conduit. From memory, I think the recommended separation distance is 350mm if comms cable is unscreened.
 
Re: Advice needed on consolidating av and coax cabling alongside five 240 volt main l

use a separate conduit.
 
Re: Advice needed on consolidating av and coax cabling alongside five 240 volt main l

Yes, i'll run another conduit. D.Skelton recommended a uniform spacing of 350mm. I'll probably run conduit along the other side, away from power lines, I thought it would save time using existing conduit but I now understand that this is not practicle.

Thanks all for your help.
 

Reply to Advice needed on consolidating av and coax cabling alongside five 240 volt main lines in the FreeSat, Sky, VirginMedia Forum area at ElectriciansForums.net

Similar Threads

I have a new combo meter box and 200A main shut off installed outside professionally. It has 4/0 service line coming into it and I have...
Replies
1
Views
1K
Was wondering if the gurus can critique and/or provide recommendations on my plan to install two sub-panels in a (50'x100') 5,000 sq ft steel...
Replies
2
Views
1K
J
Hi, I'm looking to re-join the two spurs legally and safely after the wall was knocked out under the window where the cables ran in a channel in...
Replies
28
Views
5K
ArseyDee
A
E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
77K
S
I will post the answers on here in a few day or if you really want to know PM me and i will send them. Example Questions for 2382-10 1. The...
Replies
1
Views
2K
sxsparky
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock