Hi. Brand new member looking for guidance.

Am trying to take a lease on a commercial premises but I require a lot of electricity. See attached the photo of whats already in the premises. I'm being told its only a 45 kVa supply.

I require (I think) a 300amp supply. I dont really know my watts from my amps from my kva but what I do know is that the machinery I need to run 24/7 will consume about 3000 kw per day. Its a data centre but I dont really understand the ins and outs of the electrical supply.

So the landlord has told me its 45kva (I have the MPAN if it helps) but the photos (attached) I'm told look like 3 phase. Can someone please help me the f out as I am totally clueless.

Landlord has applied for a quote to upgrade the supply which can take 4-5 weeks, and then the works up to 12 weeks. They cant even confirm IF the supply can even be upgraded which sounds odd considering another unit on the site has a "300 kva" supply. No idea what this work will cost either.

Any help much much appreciated before I sign a 10 year lease.

Ta

IMG_6188.JPG
 
I can't really help in terms of upgrading the supply but you will need to get some more exact figures with regard to load in order to work out what you need. When you say 3000kW per day I'm guessing you mean kWh? Thats would equate to 125kW of load which comes to around 550A. To run this I would think you would be looking for at least a 200A 3ph supply, more if you are planning to upgrade in the future? Best thing is probably to discuss your needs with an electrical contactor used to working with commercial/industrial to design the instalation and calculate the maximum demand and therefore the size of supply required.

As you say this will be a data centre, do you also need UPS/generator backup?
 
If you need a 300amp supply, the photo you provided shows 60-80amp fuse holders with a 40-100amp meter.

I don’t think you will be getting more than 100amp without major upheaval.

Call a spark along to look at your requirements and have a look at that Main supply a little closer.

Getting the DNO to organise you with a bigger supply won’t be cheap.
 
550A supply - that's a lot of aircon and a big server farm! What's the sq/ft of the building? Surely at that level both the HVAC plant and IT suppliers involved will have exact specs of what is needed and will have done all the sums?
 
Now I'm curious...

Data centre with computer gear that doesn't need a UPS.
..and it must be one big building for a supply that size.
I did an upgrade to 400amp for a new build printers with 2 10 colour Heidelberg printers and a load of other 3 phase equipment a few years ago.
 
You would need a new upgraded supply, the existing supply is too small. You will also need metering upgraded to CT metering, whole current only used up to 100 amp. I would check with dno to see if large enough supply is even available.
 

Reply to Advice Needed: Upgrade of Commercial Supply in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
530
Hi all, So my factory needs more power, currently 100A/3p (70KVA) => 400A/3p (200KVA) UKPN wont upgrade existing supply and are insisting on new...
Replies
1
Views
373
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
645
Got an EV (Nissan Townstar EV) in my house, has a Zappi EV charger installed (by myself) and notified via ENA form to Scottish Power energy...
Replies
4
Views
1K
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
696

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock