Search the forum,

Discuss Advice on outdoor circuit please in the UK Electrical Forum area at ElectriciansForums.net

Think through what you want now and longer term. If you can get away with a "glorified extension cable" for less than 13A it is an easy, cheap and quick route to having electric out there safely.

But if you want it more permanent, or want to have extra capacity, then get an electrician to look at it. You would end up with a dedicated circuit from your main board, but depending on the needs on reliability you might go for a fused-switch from the meter tails feeding the SWA cable instead of another RCBO.

Basically if you have a RCBO/MCB feeding the outdoor stuff you won't easily get selectivity with any down-stream protection. So if you blow a fuse on a 13A outlet it will probably trip the feeding MCB/RCBO as well as any local breakers. That may not matter to you if lights go off, etc, but in other cases it might be an issue (say you have a freezer on a 2nd circuit and you don't notice it has gone off and de-thawing everything).

However, if the feed SWA is of adequate size and so the feed fuse is relatively big (say 30A or more, but it depends on the downstream stuff) it will usually survive long enough for the down-stream fault protection to clear the fault.

Another factor in the cable / system design is if you need any earth bonding for "extraneous conductive parts" in the garage (steel structure, water pipes, etc) and you are on a TN-C-S supply (where your local earth and neutral are common up to the meter cut-out). In those cases you are required to have a minimum of 10mm copper-equivalent earth conductor size due to the potential high sustained fault currents if the PME goes open. Or you do a separate earth rod for a TT style of arrangement.

So plan what you want to do with all these factors in mind.
 

Reply to Advice on outdoor circuit please in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Im just curious as to peoples thoughts on the following install I seen on a video from an Electrical firm today and they did the following: Ran...
Replies
2
Views
557
I've had a search, and found an old thread from 2016... but was wondering about modern views on this situation. I've come into possession of...
Replies
5
Views
400
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
1K
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
356
Hi all, Curious one and hopefully some one of you could give me some advice. A customer has had a steeltech shed installed at their premises. A...
Replies
17
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock