Discuss Advice on plan (diagram included) to remotely turn on an amplifier using CAT5 in the DIY Electrical Advice area at ElectriciansForums.net

H

hatterman

Hi all,

I am currently have an amplifier that is powered by an ac/dc adapter (as shown in diagram below). In my house I have CAT5 cable run from where the amplifier is to a position on the wall (it is currently not being used). I want to be able to push a button on the wall where the CAT5 cable goes to with the result that the amplifier is either powered on or off. Would the setup in the diagram work? The adapter has two wires coming out of it (positive and neutral?), so I planned to keep the positive wire uncut and the neutral wire would be joined to the CAT5 loop with the push switch in.

Many thanks for any advice.

2itrdpi.jpg
 
Cat5 cable is designed for data, not power, so there's not enough copper cross-section to carry much current without losses. A few metres would be the maximum cable length before the amplifier starts to be affected by voltage drop. I would fit a relay beside the amplifier to control its power using a much smaller current through the switch cable. You will need three cores to the switch if it is illuminated, and if it is momentary rather than latching you will need a flip flop or bistable relay, or else the amp will only be on while you hold the button. If you are not familiar with relays etc, an electronics hobbyist friend might be able to rig it up for you.
 
your typical cat 5 cable conductors are 24 guage/ 0.55mm and the ampacity would be around 6 amps ac and around 4 amps dc, so cat 5 would not be heavy enough for this and you could risk fire.
your better off getting larger cores for this
 
24AWG is approx 0.2mm² and rated at 0.58A. Two pairs in parallel would give 0.8mm² which is sufficient for the mains adaptor output rating, so there's theoretically enough capacity. However, because they might not be reliably paralleled and more because of voltage drop, I agree it is a bad idea.
 
Have you considered using a wireless radio controlled socket adaptor and a remote control stuck to the switch position? Something like this perhaps, would allow the PSU to be plugged in close to the amplifier.
lightwaverf-remote-control-on-off-socket-3-pack-white_1.jpg
 

Reply to Advice on plan (diagram included) to remotely turn on an amplifier using CAT5 in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Looking for some cabling advice for my garden project. I’ve put together this diagram below, which hopefully explains what I’m trying to achieve...
Replies
5
Views
1K
can anyone please advise on where the wires go? My electrician installed a new cable ready for when I bought a security light. The cable as shown...
Replies
3
Views
530
(Trying again, as picture didn't post first time) Hi, I'd be very grateful if anyone could help me here. Below, I've pasted a sketch showing how...
Replies
5
Views
1K
Hi, I have ran a light ring off a fused spur with two lights on, each with their own switch (outside and lobby light) I want to put the outside...
Replies
4
Views
2K
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
430

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock