  1. Maximus Rumpas
    Offline

    Maximus Rumpas Guest

    Hi,

    I would like to ask your advice about how difficult it might be to pull cables through 20 mm plastic conduit. (easy, moderate, hard, impossible)

    I am running two separate lines for a cooker and hob in 6 mm2 single core stranded cable. Both runs will follow the same route.

    4 meter run from distribution board via 90 degree inspection bent to an inspection box next to soil stack.

    Next 2.5 meter run through Bathroom/Kitchen wall to an inspection box under sink (minor set to allow for wall levels)
    Then either
    4 meter run, chased into wall via 90 degree inspection bend to a third inspection box.
    or
    4 meter run via 300 mm drop to Floor level - two 90 degree inspection bend to the third inspection box.

    Lastly 1.5 meter run to cooker or hob isolation switch.

    On completion permanent access to inspection boxes - limited access to 90 degree inspection bends.

    Your thoughts please.

    Kind regards
    Max
     
  2. Sintra
    Offline

    Sintra The Innkeeper Staff Member Admin

    Location:
    Belfast/London
    Mate they make conduit in larger sizes than 20mm. I would go 25mm.
     
    • Like Like x 1
  3. Maximus Rumpas
    Offline

    Maximus Rumpas Guest

    Thanks Sintra,

    Due to limited clearance in some areas I would like to avoid using a larger conduit if it were possible to use 20mm. If the advice is that it is impractical then I will have to use a larger size.

    Max
     
  4. gazzaabc
    Offline

    gazzaabc Guest

    I'm not understanding you? Can't you just tell us how many cables are in any one conduit and the sizes of the cables? You will struggle with 6mm in 20m conduit a specially with a bend. I think that's a no go
     
  5. ayjay
    Offline

    ayjay Guest

    Location:
    north korea
    you need 25mm and a spring to bend it and some lube
    or use singles,not twe
     
  6. gazzaabc
    Offline

    gazzaabc Guest

    [email protected] the lube technique :) fairy does the trick every time. U will get 10mm if you use fairy lol jokes
     
  7. Maximus Rumpas
    Offline

    Maximus Rumpas Guest

    Hi Gazzaabc,

    I thought I had - separate feeds to cooker and hob in 6 mm2 single core stranded cable Live, neutral and a smaller earth. Three cables in total in one conduit run. I thought I might struggle and that I should go for 25mm but wanted to check first.

    Kind regards
    Max
     
  8. Maximus Rumpas
    Offline

    Maximus Rumpas Guest

    Hi ayjay,

    Never mentioned twin and earth. Question stated single core.
     
  9. gazzaabc
    Offline

    gazzaabc Guest

    If the earth is smaller you will defo get 3 cables down a 20m pipe if only 2 of them are 6mm. You won't even struggle
     
  10. gazzaabc
    Offline

    gazzaabc Guest

    Max if your using plastic pipe you can buy 2 types of elbows! Buy the larger type. it's a bigger and longer bend but its not as harsh on the bend as the smaller one and makes life a lot easier.
     
  11. Sintra
    Offline

    Sintra The Innkeeper Staff Member Admin

    Location:
    Belfast/London
    OP stated "I am running two separate lines for a cooker and hob in 6 mm2 single core stranded cable. Both runs will follow the same route." I am taking this as 2 circuits 6 x 6mm singles.
     
    • Like Like x 1
  12. Maximus Rumpas
    Offline

    Maximus Rumpas Guest

    Hi Sintra,

    O, I see how I might have confused you, sorry. One run for the cooker and a second for the hob. each conduit carries 2 x 6 mm2 + 4 mm2 earth. Apologies to all.

    Max
     
  13. Sintra
    Offline

    Sintra The Innkeeper Staff Member Admin

    Location:
    Belfast/London
    All clear now lol.
     
  14. ipf
    Offline

    ipf Forum Mentor

    One's an elbow, the other a bend.........I believe!
     
  15. GLENNSPARK
    Offline

    GLENNSPARK Electrician's Arms

    Location:
    west yorks.
    washin up liquid eh?.....jesus wept...don`t you dare!!
    to the O/P.....go and get some 77........
     
Loading...
Similar Threads - Advice Pulling single Forum Date
Domestic I need advice with light loop Lighting Forum Today at 9:04 AM
Irwin Hilmor Pipe Benders Advice. Electrical Courses & Electrical NVQ's Today at 12:00 AM
Thread Status:
Not open for further replies.

Share This Page

Users found this page by searching for:

  1. how many 6mm singles on a 20mm conduit

Electricians Directory Post a Domestic Job Post a Commercial Job