T
The Ghost
It does niggle me that the rn/r1/r2 are not showing in the report.
Discuss Advice on Unsatisfactory EICR report in the UK Electrical Forum area at ElectriciansForums.net
It does niggle me that the rn/r1/r2 are not showing in the report.
I think I purged the EICR of any identifying info, so £245, no VAT.Any chance on getting the EICR price?
I think I purged the EICR of any identifying info, so £245, no VAT.
Interestingly, I found the previous EICR,Id bet my 50p that zero dead testing was carried out.
About 4.5 hours for £245How long were they on site?
ReadingLondon?
I think it's spelt Scouser...Sponge scourer.
Interestingly, I found the previous EICR,
- it has the r1, rn, r2 values on the ring mains.
- and it had 1mm cable for lighting circuits which I don't believe. This may have just been copied into the new EICR.
- the IR tests on the ring mains and lighting was not done due to "unable to remove all load sockets, lighting had electronic dimmers"
There's still a dimmer upstairs, but it's downstairs lighting that has the supposed earth leakage.
I actually think the questions are reasonable. The op did not mention that they are not having the work done.Take the money for the rent but unwilling to spend money to keep the people inside safe.
I think if previous r1,rn,r2 readings are available then these tests can be omitted if needed.
I'm sure I heard that on the 2391 course. I could be wrong
No. Always test ring continuity on EICR mate as it needs to be confirmed as part of proving if circuit is satisfactory or not.
This is actually mentioned in gn3 if it looks like the ring has not been altered and there are previous test results,however I’d always test it as standard.Think there is something about this in one of the books. I'll see if I can find it
Reply to Advice on Unsatisfactory EICR report in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.