I’m hoping that somebody could give me some advice.

We recently had a new kitchen fitted, we had an excising double which is 4.1kw. This was wired into a consumer unit and a deducted cooker ring MTN132 B32 - 32amp breaker.


Our new induction hob is 7.4 kw.


The contractor has used the same feed from this supply to provide power for both my oven and induction hob. There are switches that isolates both appliances.


It is now been suggested somebody else, that this is incorrect, and that they should have ran a totally new power supply to the board. Reason being that it could trip the board if we use all our appliances, for example at Christmas or worse may be dangerous.


I have tested the system, in the best way I can by having all the appliances on and using all the hobs over a prolonged period. So far, all is good with no obvious issues.


Please can anybody advice me on weather I should start again and have a new supply to the induction fitted?


Thanks in advance.
 
assuming that the circuit cable is 6.0mm, then it will be fine. that's because you never have all elements drawing current simultaneously, due to the fact that, even if all options are turned on, the stats willl be switching on and off, so the average load is well under the max. rating of the appliance/s.
 
Vortigern - you are correct, I need to check my spelling. Induction and existing.

Spoon - it was another election who when I was speaking to him over the phone re another matter expressed concern stating that the hob alone was 32amp so how could the 32amp circuit handle the oven too which was 4.2kw.

Telectrix - thank you for your reply. Yes it is 6mm cable. I have been having a few sleepless nights thinking I’m going to have to run a new supply to my hob/and or oven.
 
Just add, when checking the maximum load for a new induction hob for a client, the brochure mentioned 'zoning' of the heating rings. It would appear this particular hob is able to run two rings together. Why, I have no idea! The manufacture, Neff gave slightly higher ratings, than the normal diversity calculous would normally give.
 
domestic ovens do NOT generally pull high current. in fact, most come fitted with a 13A plug top these days.
 
Thanks again for all your posts. My particular oven is 4.1kw, the induction hob (AEG) is 7.4kw, 32 amp in its own right.

At the moment, and having tested with all jobs in full power and both ovens on full heat, the board had not tripped.

My primary concern of course is safety. It’s seem that their is a split opinion on if there should be a separate cable required.

Talking to another electrician earlier he could not understand the theory diversity. He had a black and white view of if your hob is 32amp and your board breaker/fuse is 32amp how can this be right?

You have probably gathered, I have no idea about electrics so pur my faith in those who have this trade craft and expertise.
 
cooker diversity works like this:
say your total rating comes to 40A.
load (A) = 10A + 1/3 of remainder
i.e 10 + 10 = 20A (+5A if cooker isolator incorporates a 13A socket).

this is due to the fact that, even if all elements are switched on, each will be cycling on/off at different times.
 
Right, thank you. So in my case both my combined appliances, oven and hob equates to 11500kw. Taking that into account and factoring in that 6mm is in use makes the 32amp rcd prictected board breaker/fuse suitable?
 
Right, thank you. So in my case both my combined appliances, oven and hob equates to 11500kw. Taking that into account and factoring in that 6mm is in use makes the 32amp rcd prictected board breaker/fuse suitable?
 
i hope you meant 11500watts, not 11500kW. :(.
in which case, it's 10A + 13A = 23A design current. ( add 5A if a socket is on the isolator ).
 

Reply to Advice re oven and hob wiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
768
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
591
hi looking to install a new induction hob to current wiring . the wiring i have is thick white probably about 15mm wide and is hard wired into...
Replies
0
Views
856
Hi all We are hoping to upgrade our oven. We currently have a single integrated oven and a separate induction hob. Each has its own red switch...
Replies
0
Views
795
Hello, I’ve got an issue driving me crazy and can’t get anyone to figure it out as it’s not their issue. We had a new extension, single rear...
Replies
9
Views
982

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock