Sirob

I have just replaced the PowerRail 300 with the 303, used existing CT's, 3 phase installation in small work shop. This is the first time that I have completed this type of installation

The Customer states that the reading is higher than expected, CT set to 100 amp. I am a little stumped to why this is occurring, any advice offered gratefully received.
 
I presume you have to configure the new one for the CTs you are using?

I guess they will accept multiple ratios of CTs like other ammeters.
 
I wouldn't know what a power rail 303 was if it hit me on the head but a quick look suggests it's like any other configurable ammeter.

Screen shot from the imstructions.

IMG_2419.PNG
 
Hi thanks for reply
Yes read this and set ct to match nominal primary of current transformer
Which appears to be 100amp as 3phase supply
So as said set up looks right!
Has anyone got any experience with these meters,and ct's ?
Thanks sirob

IMG_0478.JPG
 
The ring the manufacturer.

How far is it out? Have you a calibrated clamp on you can measure the actual load and use the fine tune facility?

Maybe it correct and the client is wrong. Maybe the old one was never right.
 
Hi the client is making things difficult by not knowing previous bills
Which I'm abit confused about and as you say not sure if ever worked as it should! Plugged a 3kw bar heater in to check function and the reading on the meter was just slightly over, the difference was nothing really
But I could try fine tuning the ct,s down but is does say use ct primary 100amp, client read meter Monday morning found the unit to have used 8 units and can't work out why readings so high in such a small time fram
 

Reply to Advice required on PowerRail 303 kWh & kW Meter in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Edited - please read right to the end! Grateful for any advice regarding CT metering which seems to be generating inaccurate/implausible...
Replies
25
Views
3K
I have a few questions on a service upgrade project. I am working on a ~100 yr old tri-plex in washington state. The existing panels (3) have...
Replies
11
Views
2K
I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
Replies
54
Views
6K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock