I’d look at burying tape rather than rods and create an Earth nest.

I got a c asking Ra last week even with all the sun we’ve had.
0.74ohms can't be going through the earth surely, did you touch the water supply pipe on the way down and are going back to the network via someone else's bonding?
 
0.74ohms can't be going through the earth surely, did you touch the water supply pipe on the way down and are going back to the network via someone else's bonding?
I didn't install it, only tested it, it's been in the ground 15 years.

I reckon it's hit another service on its way down, according to the paperwork the rod is 5/8" and 3m long so not a twig by any means.
 
Got to page 403 then gave up

Fore warned ..403 Went straight to appendix-es ..
Now getting bored with list .

EARTH ELECTRODE SUBSYSTEMS -- 11, 24, 25, 31, 33, 44, 51, 52, 63, 64, 65, 66, 70, 7 1 , 85, 86, 87, 8 9 , 101,
107, 120, 131, 137, 138, 145, 148, 170, 187, 190, 196, 205, 212, 213.

213 ..FAIL ..mostly surface corrosion /good connection (+ RF Impedance)

.... Then got side tracked with memories "Things wrapped in Brown wax paper ,in heat sealed polythene bags..."
( may see if my -Inner lucky stumble , is working later )
 
Managed to get it down to 112 Ohms, after paying out a small fortune, 3 earth rods later all connected with flat copper tape (25mm x 3mm x 25m) dug into the ground about 12” deep, couldn’t get any deeper due to roots and rock. Thanks guys for the advice
 
Managed to get it down to 112 Ohms, after paying out a small fortune, 3 earth rods later all connected with flat copper tape (25mm x 3mm x 25m) dug into the ground about 12” deep, couldn’t get any deeper due to roots and rock. Thanks guys for the advice
Cool, go back when you've had a couple of days rain and test again, just out of curiosity.

Personally I wouldn't have bothered with rods and gone solely for tape.
 
Am I missing something ? Why the need for such low readings, gn3 anything under 250 ohms is acceptable but in theory fine up to 1667 book not to hand so may be wrong?
 
Am I missing something ? Why the need for such low readings, gn3 anything under 250 ohms is acceptable but in theory fine up to 1667 book not to hand so may be wrong?
1667 is only relevant to circuit/s downstream of RCD/s.
 
Am I missing something ? Why the need for such low readings, gn3 anything under 250 ohms is acceptable but in theory fine up to 1667 book not to hand so may be wrong?
Agree with you the 1667, but if over 200ohms it is deemed unstable or words to that effect.
I haven't got my book to hand,but I'm not to sure about your 250 figure.

I had a 207 ohm Ze last week but let it go due to extremely dry whether. It had the additional protection of 30 ma rcd so in theory yes the 1667 would have been ok.
 
Stima, the main reasons for the extra earth rods were to fix the ends of the tape to them, mainly for testing, I just wanted to have each end of the triangle that I have made a testable point, just for my own peace of mind, the highest vale tested was what I recorded nearest the property anyway and it’s much lower away from the property when tested at the other two earth rods, it’s a tad over kill I know but much better now than the 1.8k that I could not get lower reading off and wanted a true reading to be as low as possible without having to water the rods which I feel is not really a true reading as no one will be watering the earth rods on a daily basis and wanted the readings to stand up on dry, hot days like we have now.
 
Earth Rods are being hit in to their entire length, approx 1m deep, cannot get much deeper as we are hitting bedrook, have tested using |KEW-5105A and then tried removing the earth rood and testing again 1 meter further away from the property and so on, but cannot get the reading to get any lower. The soil is not the best, looks as though its had about 100 years of tiles, bricks and plaster pored into it.

Sounds to me you are doing loop testing not Ra testing(?)
 
In a case like this, the readings will be identical for all practical purposes.

Can you really say that? Ra testing would only be between the rod he has installed which he said was 1M down and 10 meters away while the loop test will be the Ra plus the full loop.

An Ra test is a dead test and a loop test is a live one.
 
Can you really say that? Ra testing would only be between the rod he has installed which he said was 1M down and 10 meters away while the loop test will be the Ra plus the full loop.

An Ra test is a dead test and a loop test is a live one.

But in this case (and most others), the rest of the earth fault loop will add very little impedance on top of that provided by the interface between the rod and the bulk of the earth. So the difference between Ra and Ze will, in most cases, be negligibly small.
 

Reply to Advice Wanted - VERY High Earth Resistance Problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
522
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
968
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hello fellow professionals, I'm currently facing a challenging scenario that involves the integration of solar photovoltaic (PV) systems on roofs...
Replies
1
Views
264
Morning all, Really hoping to get some advice / confirm what a few of us are thinking about a job in the future. Back ground - We have to swap...
Replies
15
Views
385

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock