    Does anyone know the working method the supply companies use to calculate after demand diversity.
    Most new houses are supplied with 100amp fuses in the cut out.
    Now obviously the average houses don't come anywhere near using that amount of current, however the DNO must allow a working average current for each phase.
    The iet design guide gives a little insight but wanted to know other people's thoughts.
     
  2. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    A colleague used to do design and he told me for a housing estate you would allow 6A per dwelling but that was about 15 years ago.
     
  3. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    6amps seams really really low.
    We've got 14 flats on a floor and we are fitting a bemco to each floor 6 in total.
    16mm swa has been specked to each flat and 40 amps per flat which is really generous as each flat is only 1 bedroom and only have 2x 1.5kw heaters in and an immersion.
    I'd say more like 20 at the most.
     
  4. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    It was a while back but it must have worked.
     
  5. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Hi - here's some After Diversity Maximum Demand numbers from a DNO design spec, just FYI.

    IMG_0655.JPG
     
    • Like Like x 1
    • Friendly Friendly x 1
  6. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    I'll come up with a design with my boss and speek to the DNO and consultant about requirements.
    At the end of the day I don't want to be pulling in unnecessary large cables.
     
  7. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    Thanks wilko will have a look
     
  8. chris day
    Offline

    chris day Regular EF Member

    Location:
    london
    Business Name:
    Chris peter
    Keep us posted on your findings as I have also wandered how to apply for diversity on flat sub mains
     