The MV side of the TX protection, is normally sensed from the LV side, via protection relays!! Which is why i asked if there was an DNO LV switchboard in the substation. 3m doesn't seem long enough to connect directly onto the TX LV connection bushings/bars. Could also be the location of the protection CT's, (if any) on those LV bushings. Weird set-up all round if what the OP is saying is correct...lol!!
 
only reason i asked about length of lv cables was because we did something similar lv was 12mtr with no protection ,but we were installing a c/o panel and installing new 630mm singles 22mtr run we had to install new acb cubicle near tx
 
Where do these 3m of tails connect to in the substation, directly to the Transformer or to a LV DNO Switchboard??
I can't believe there is absolutly no protection provided between the TX LV terminals and your unprotected main switch!!! Loops as you call it, are normally only seen at the MV/HV side of transformers, by means of RMU's (Ring Main Units)....

My advice, is to get a Qualified Electrical Engineer involved in your planned project now, tell him your requirements, and let him make the dicissions on how to go about achieving them in a cost effective way... Or, Panel manufacturers can also be given the task of providing your needs. Who will send an Electrical Engineer to assess what you have, and what you need and propose a design to meet them, based on/around their panel systems... You could ask 2 or three such manufacturers to quote on your project.

And ask the Engineer to do a discrimination study on the whole set up by the looks of things...
 

Reply to Air Circuit breakers in the Canada area at ElectriciansForums.net

Similar Threads

Background Two weeks ago, lightning struck a tree in our yard. Many circuits tripped and several electronic devices failed. There was a strong...
Replies
2
Views
836
Apologies up front but I'm a DIYer and only got 1 reply on that forum so trying here. I'm in Ontario Canada where a homeowner can do there own...
Replies
2
Views
851
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
Hi! I’d like to install a pedestal-mounted (230 V, 30 A max - programmable) EV charger close to my driveway, which ends about 12 feet away from...
Replies
1
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock