Discuss AM2 a few revision questions in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
7
Im taking my AM2 on Monday and have a few questions just to get my testing on point. Firstly when testing continuity of cpc would a the assessor expect each cpc to be connected to the line conductor in a connector block for example (separately from the earth bar to eliminate parallel paths)? Or would a link from the earth bar to the load side of the circuit breaker for each circuit be acceptable?

Also when testing polarity do you think that the assessor would be happy for this to take place while testing Continuity of Cpc or would he/she expect it to be done after insulation resistance (as the sequence of tests is written)?

Also when testing PSCC on a 3phase install GN3 says if the meter being used can test between for example two phases (L1+L2) then the highest reading should be divided by 0.87 am i reading this correctly? As i have always only been told to double the highest reading when using a meter than cannot test between two phases.

With safe isolation (dont want to fall at the first hurdle) should the main distribution board be safely isolated and locked off before removing the cover? Because either way it will have to be reenergised (with the lid off) when testing PFC anyway or am i wrong?

Thanks
 
The preferred method of testing continuity is R1+R2 (Method 1 in guidance note 3 - the reason will become apparent in a mo). Since you are testing a new installation, you should know whether there are parallel paths present. I took the CPC out the block and linked it to the line using an assessment centre provided Wago.

Polarity... Guidance Note 3 (familiarise yourself with it so if asked you can point the assessor to it) states you can prove polarity through a combination of visual inspection and R1+R2 testing.

What you're interested in is the Prospective Fault Current. It is acceptable to measure this from Line-Earth for each phase, take the highest value and double it. In reality you would, if your meter is capable, test between phases but in the AM2 it's acceptable to measure Line-Earth and double up the highest.

Just as you'll probably be advised to calculate Zs. In reality I like the security of measuring it but for the AM2 where time is short, you calculate it using the highest Ze value, but remember to add a remark to each line of the cert saying "Zs by calculation".

You will do two sections of safe isolation. I found it wasn't possible to remove the board cover with the lockout device on, so for the first stage (which is effectively proving your bay is safe for you to work on - this is done with the risk assessment section) I turned the board off (don't forget to ask if this is OK), took the cover off, locked it off, proved dead. The board cover then did not go back on my install bay until I had finished the testing that required access to it. For the other section (which in my case preceded the fault finding) there are three scenarios where you have to do safe isolation... two are isolating circuits in preparation for working on them... do not take the cover off the board for these.
 
The preferred method of testing continuity is R1+R2 (Method 1 in guidance note 3 - the reason will become apparent in a mo). Since you are testing a new installation, you should know whether there are parallel paths present. I took the CPC out the block and linked it to the line using an assessment centre provided Wago.

Polarity... Guidance Note 3 (familiarise yourself with it so if asked you can point the assessor to it) states you can prove polarity through a combination of visual inspection and R1+R2 testing.

What you're interested in is the Prospective Fault Current. It is acceptable to measure this from Line-Earth for each phase, take the highest value and double it. In reality you would, if your meter is capable, test between phases but in the AM2 it's acceptable to measure Line-Earth and double up the highest.

Just as you'll probably be advised to calculate Zs. In reality I like the security of measuring it but for the AM2 where time is short, you calculate it using the highest Ze value, but remember to add a remark to each line of the cert saying "Zs by calculation".

You will do two sections of safe isolation. I found it wasn't possible to remove the board cover with the lockout device on, so for the first stage (which is effectively proving your bay is safe for you to work on - this is done with the risk assessment section) I turned the board off (don't forget to ask if this is OK), took the cover off, locked it off, proved dead. The board cover then did not go back on my install bay until I had finished the testing that required access to it. For the other section (which in my case preceded the fault finding) there are three scenarios where you have to do safe isolation... two are isolating circuits in preparation for working on them... do not take the cover off the board for these.
Thanks alot mate!!
 
What you're interested in is the Prospective Fault Current. It is acceptable to measure this from Line-Earth for each phase, take the highest value and double it. In reality you would, if your meter is capable, test between phases but in the AM2 it's acceptable to measure Line-Earth and double up the highes
You must also measure each line to neutral, double the highest of the readings
 

Reply to AM2 a few revision questions in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
My garden lighting was tripping my MCB so I checked all the junction boxes outside. I disconnected the live, neutral and earth connections in...
Replies
2
Views
850
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock