Hi everyone,
Not going to lie I am crapping my self for my AM2 exam on Monday Morning at 8:00. So I just need a few questions answered:- tell me if I am right or wrong.
I will be using a megger tester by the way.
PEFC testing 3 phase ( 3 probe test) :-
Clamp croc clip on the neutral bar.
L1-N -E
L2-N-E
L3- N -E
People say do to simply:-
L1-E
L2-E
L3-E
Keep a mental note of the highest figure.
PSCC on 3 phase ( 3 probe tesy but, put the neutral test lead/probe into the earth test probe so its now a 2 lead test)
Test between:-
L1-N
L2-N
L3-N
Mental note of highest figure.
Out of both test the highest figure is doubled as a rule of thumb as the fault current could occur between two phases. This fig is recorded on the test sheet as IPF.
For testing a RCBO on lighting circuit people say disconnect the load and carry out IR seperate, but also still test the RCBO tripping times but how would you do that? As in the exam you are not aloud to expose any live conductors during the live tests.
Also, when doing IR test you have to disconnect certain equipment. But, when doing the ring main there is outdoor socket with a neon fused spur in. How do you disconnect the neon out of the socket. Can you simply out the connections to this socket in a wago connector and put the socket back on, as there will be no conductors connected to the outdoor sockrt. But, I am still testing the conductors?
Any help would be great!
HELP!
Not going to lie I am crapping my self for my AM2 exam on Monday Morning at 8:00. So I just need a few questions answered:- tell me if I am right or wrong.
I will be using a megger tester by the way.
PEFC testing 3 phase ( 3 probe test) :-
Clamp croc clip on the neutral bar.
L1-N -E
L2-N-E
L3- N -E
People say do to simply:-
L1-E
L2-E
L3-E
Keep a mental note of the highest figure.
PSCC on 3 phase ( 3 probe tesy but, put the neutral test lead/probe into the earth test probe so its now a 2 lead test)
Test between:-
L1-N
L2-N
L3-N
Mental note of highest figure.
Out of both test the highest figure is doubled as a rule of thumb as the fault current could occur between two phases. This fig is recorded on the test sheet as IPF.
For testing a RCBO on lighting circuit people say disconnect the load and carry out IR seperate, but also still test the RCBO tripping times but how would you do that? As in the exam you are not aloud to expose any live conductors during the live tests.
Also, when doing IR test you have to disconnect certain equipment. But, when doing the ring main there is outdoor socket with a neon fused spur in. How do you disconnect the neon out of the socket. Can you simply out the connections to this socket in a wago connector and put the socket back on, as there will be no conductors connected to the outdoor sockrt. But, I am still testing the conductors?
Any help would be great!
HELP!