Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Discuss Amendment 3 and Upfront RCD/Overcurrent protection for TT Submain in the Electrical Forum area at ElectrciansForums.co.uk.

Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. shaun1
    Offline

    shaun1 Regular EF Member

    Location:
    United Kingdom
    Hi all,

    Currently looking for something to protect a Sub Main in a house. Supply is TT and consumer unit is to be located aprox 10m away from the incoming service. Sub main will be 25mm armoured, and all final circuits will have RCD protection.

    As far as I can see, I will still need an up front 100mA RCD to provide fault protection, along with an 80A Fuse for overcurrent (and fault) protection.

    Is there an all in one procuct to achieve this? If not, there is currently a plastic 4way enclosure with a suitable RCD inside, but as everything else is to be replaced/re wired, I assume this will need to br replaced for a non conbustable kind? If we replaced the enclosure with a metal one, are there suitable tail clamps for the incoming meter tails, or would a plastic gland be acceptable?
     
  2. Pete999
    Online

    Pete999 Forum Mentor

    Location:
    Northampton
    Business Name:
    None
    British General Plastic Gland Kit 2x16mm² + 1x16mm² Tails Cable | Consumer Unit Accessories | Screwfix.com - https://www.screwfix.com/p/british-general-plastic-gland-kit-2x16mm-1x16mm-tails-cable/6037p
     
  3. Pete999
    Online

    Pete999 Forum Mentor

    Location:
    Northampton
    Business Name:
    None
    British General Plastic Gland Kit 2x16mm² + 1x16mm² Tails Cable | Consumer Unit Accessories | Screwfix.com - https://www.screwfix.com/p/british-general-plastic-gland-kit-2x16mm-1x16mm-tails-cable/6037p
     
  4. Leesparkykent
    Offline

    Leesparkykent Super Moderator Staff Member Super Moderator

    Location:
    Kent
    Lewden switch fuse, change the main switch in the switch fuse for a 100mA S type RCD and gland the tails using a nylon tail gland.
     
    • Agree Agree x 1
  5. Des 56
    Offline

    Des 56 Forum Mentor

    Location:
    Gliese 581C
    The Iet have given guidance on TT tails
    They can be connected directly to a metal clad board before the Rcd as long as the tails have enhanced protection

    I personally would fit a S type Rcd in a plastic enclosure fed by the tails, then on to the metal clad switch fuse
    A bit junkier but a lot safer in my opinion
     
  6. shaun1
    Offline

    shaun1 Regular EF Member

    Location:
    United Kingdom
    Perfect. This is what I was after. Just to confirm, one of these will fit in here, and I will have a suitable bit of busbar etc from the main switch?
     
  7. Leesparkykent
    Offline

    Leesparkykent Super Moderator Staff Member Super Moderator

    Location:
    Kent
    Yeah...The more recent version had a metal hinged flap rather than the plastic one like in the link.
     
Loading...
Similar Threads - Amendment Upfront Overcurrent Forum Date
1st Amendment to 18th 2020 Electrical Forum Feb 7, 2019
18th edition amendment 1 Electrical Wiring, Theories and Regulations Feb 7, 2019

Share This Page

Users found this page by searching for:

  1. 80a overcurrent protection

Electricians Directory Post a Domestic Job Post a Commercial Job