Discuss An interesting exchange today with Contactum, IET & NAPIT in the Certification NICEIC, NAPIT, Stroma, BECSA Forum area at ElectriciansForums.net

It might be a good idea to involve Bomb Disposal in this because it looks very much like we're all stood at the edge of a great big minefield.
 
There is still great confusion all around here and IET has yet 'to my knowledge' to give a definitive response to the questions posed to them about the confusion of this regulation 421.1.201

Here lies the problem - The consumer unit or similar switchgear has to comply to BS EN 61439-3 with basically is a set of test like an hot touch, self extinguishing etc...

As worded by the regs - 421.1.201

Within domestic (household) premises, consumer units and similar switchgear assemblies shall comply with BS EN 61439-3 AND SHALL;

(i) have their enclosure manufactured from non combustible material, OR
(ii) be enclosed in a cabinet or enclosure constructed of non-combustible material and complying with reg 132.12.

NOTE 1: Ferrous metal , e.g. steel, is deemed to be an example of a non-conbustible material
NOTE 2: (Just mentions implementation date jan 2016)


Now the problem here is the regulations states it has to comply to both the BS61439-3 and be non combustible if you do not house it as to point (ii) but there's no documented definitive definition of a non-combustaible material but they do give an example so this is not saying it has to be steel.

My next point is everything is combustible given high enough temperatures and the conditions to burn so we need to know the exact requirements to be given a non combustible rating are.... all the manfacturers have to comply to is the BS 61439-3 and that allows them to meet the first part if the regulation but who is going to define the parameters of the word non combustible, yes steel is an example but as this is the only example they give we are stuck with the example as we have no other information to go on.
 
Last edited:
There is still great confusion all around here and IET has yet 'to my knowledge' to give a definitive response to the questions posed to them about the confusion of this regulation 421.1.201

Here lies the problem - The consumer unit or similar switchgear has to comply to BS EN 61439-3 with basically is a set of test like an hot touch, self extinguishing etc...

As worded by the regs -

Within domestic (household) premises, consumer units and similar switchgear assemblies shall comply with BS EN 61439-3 AND SHALL;

(i) have their enclosure manufactured fromnon combustible material, OR
(ii) be enclosed in a cabinet or enclosure constructed of non-combustible material and complying with reg 132.12.

NOTE 1: Ferrous metal , e.g. steel, is deemed to be an example of a non-conbustible material
NOTE 2: (Just mentions implementation date jan 2016)


Now the problem here is the regulations states it has to comply to both the BS61439-3 and be non combustible if you do not house it as to point (ii) but there's no documented definitive definition of a non-combustaible material but they do give an example so this is not saying it has to be steel.

My next point is everything is conbustible given high enough temperatures and the conditions to burn so we need to know the exact requirements to be given a non combustible rating are.... all the manfacturers have to comply to is the BS 61439-3 and that allows them to meet the first part if the regulation but who is going to define the parameters of the word non combustible, yes steel is an example but as this is the only example they give we are stuck with the example as we have no other information to go on.

my thoughts exactly. a titanium enclosure would be non-combustible, and so would a ceramic one. it's time the IET pulled their collective fingers out of their ears and came up with suitable materials, instead of just saying that steel is an example.
 
Try BS EN 60695-2-10,11&12 and BS EN 13943 for that definition DW.

It's quite clear I think :)

I myself and the majority of the normal average sparky do not have access to all these regulations to cross reference the clarity of said regulation, my point is the regulation is at best ambigious and confusing and as this applies to domestic only it should be really made clearer within the BS 7671 and in its present format you are left with anything steel or similar to be sure you have met the regulation.

If the IET deem anything complying to BS61439-3 is what part of the requirement is, then why add that its needs also to be non-combustible surely meeting these requirements minimises the dangers of a fire using the enclosure to get a hold and spread .... if the BS61439-3 isn't good enough on its own then why not raise the bar as to the requirements at manufacturing level and leave the BS7671 with a simple regulation that is easy to follow..... I just think this whole situation has been poorly introduced leaving many questions that just are not been answered.

What is the point if you can have a plastic board that complies to BS61439-3 then saying oh yeah and its to be non-combustible.. who says when a plastic board is or isn't non combustible --- I thought that was the whole point of the BS61439-3 standard hence this regulation is just a ball of confusion.
 
Last edited:
You're right, it's a joke

I think a farce is more accurate.

Its about time the IET got its act together and placed "proof reading" of their regs in the hands of the "plain english society" before the next versions go to print.

We are not all in agreement, the wholesalers don't know either, so god help Joe Public
 
just about to start up in production of CUs made entirely from glass.

1. glass is non-combustible.

2. end user will be able to see the poor terminations made by the Electrical Trainee's and avert a fire by calling in a competent electrician to fix it before a fire breaks out.

SORTED.
 
just about to start up in production of CUs made entirely from glass.

1. glass is non-combustible.

2. end user will be able to see the poor terminations made by the Electrical Trainee's and avert a fire by calling in a competent electrician to fix it before a fire breaks out.

SORTED.
Until you drop it!
 
Try right click on it and open in a new tab then you should be able to click on it again to enlarge.
 
Had a conversation at wholesalers today. They are stopping providing the old CU's. New wylex m/clad 10w HI £80 without breakers.
Wylex 40mm gland for tails £10, others available for £5. Some sort of sealed unit for rear incorporating glands £30....so we're talking something like £160 for a complete unit. Double the cost.
Looks like there's not going to be much choice. Short and curlies, eh? Ridiculous!!
 
Had a conversation at wholesalers today. They are stopping providing the old CU's. New wylex m/clad 10w HI £80 without breakers.
Wylex 40mm gland for tails £10, others available for £5. Some sort of sealed unit for rear incorporating glands £30....so we're talking something like £160 for a complete unit. Double the cost.
Looks like there's not going to be much choice. Short and curlies, eh? Ridiculous!!

Just fitted a metal wylex split board for less than £120 in parts - 8 x mcb and a 40mm stuffing gland, you're getting ripped if its £160 the wholesaler was even taking about a fully loaded soon for less than £100 so not sure where your getting yours from.
 
Last edited:

Reply to An interesting exchange today with Contactum, IET & NAPIT in the Certification NICEIC, NAPIT, Stroma, BECSA Forum area at ElectriciansForums.net

Similar Threads

I recently had a quick glance at a colleague’s Napit’s version of their on-site guide “Napit On-site Solutions Practical Solutions to Electrical...
Replies
9
Views
2K
NAPIT Certification Scheme NAPIT with more than one operative
Hi Guys Hope this is in the right place... I have recently joined NAPIT and had my assessment. We are a limited company of two qualified...
Replies
1
Views
2K
Had an email tosay saying the elecsa brand is being retired. Seems it was sent to all NICEIC sparks aswell. They are moving all the elecsa firms...
Replies
12
Views
3K
  • Sticky
Is STROMA now owned by Certsure along with NAPIT, NICEIC and ELECSA? Edit: NAPIT took over Stroma. Certsure operate NICEIC, ELECSA and NICEIC...
Replies
18
Views
11K
NAPIT Certification Scheme Work for assessment
Hi. I've got all my qualifications and want to do more work for myself. The only work I've got to show for assessment on the cps scheme is work...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock