Any quick calcs to get a rough estimate min Zs allowable for protective devices MCB, BS-88 etc, Im thinking in an exam saves time even looking at the tables if there's a fast ball park check rule of thumb.
 
Zs < V/ 5In for B type. e.g.for a 32A . Zs < 230/(5 x32) i.e. 230/160 = 1.4375. ( then apply correction factors).
Zs < V/10In for C type.
Zs < V/20In for D type.
 
Not sure how these quick calculations will save you time if you have the Tables to hand, it is just something else to remember.
 
not forgot. stated in post to apply correction factors.

anyway, cmin is to allow for voltages below 230V. what about when the voltage is > 230V. ????
 
agreed. was just considering the 0.4 secs, as most circuits (apart from distribution ccts) are 0.4,
 
We have to use the worst case scenario as given in the regulations or use manufacturers data.
As we know the voltage measured could be anywhere between 230-250 v or whatever really.
You know what they are like regarding changing regulations and moving the goalposts
 
makes you wonder why installations done before the advent of digital test meters ever managed to survive , when readings were +/- 0.5 ohms on an AVO8
 

Reply to Any quick calcs to get a rough min Zs allowable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
77K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock