Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Discuss Any Recomendations for a UPS Power Supply? in the Electrical Forum area at ElectrciansForums.co.uk.

Thread Status:
Not open for further replies.
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. Davisonp
    Offline

    Davisonp Regular EF Member

    Location:
    Amersham
    Business Name:
    Absolutely All Electrical LTD
    Hi,
    Can anyone recommend a low cost UPS to clean up a power supply?
    Also, I was wondering if a UPS would synchronise the output sine wave phase to the input phase?
     
  2. Pete999
    Online

    Pete999 Forum Mentor

    Location:
    Northampton
    Business Name:
    None
    If you are looking for a clean supply rather than a back up supply, why not go for a Motor/Alternator set up or a Voltage Stabiliser
     
    • Like Like x 1
  3. HandySparks
    Offline

    HandySparks Forum Mentor

    Location:
    Hampshire
    Business Name:
    Neish Electrical Services
    A power rating and a bit of background info would help.
     
  4. Davisonp
    Offline

    Davisonp Regular EF Member

    Location:
    Amersham
    Business Name:
    Absolutely All Electrical LTD
    I have been asked to investigate a problem with 12V thin client computers not booting (blue light comes on when button pressed, but the computer then shuts down).
    The IT team are convinced there is a “Fault” in the supply somewhere.
    Investigating the issue, if the computer is moved from the office to another part of the building and plugged in, the computer boots successfully.
    The existing transformer is outputting 12.6Volts.
    There is no problem on the ring so it appears there is an issue with the supply, which could be a nightmare and very expensive to find and fix.

    The existing supply has an output max of 36 Watts (3 Amps at 12Volts). There are 5 computers in one room, and 4 in another but there could be multiple UPS’s if required.

    The UPS is only being used to clean the supply, nothing else.

    I have recommended trying with a regulated 12Volt power supply instead of the supplied unregulated supply and see if the superior supply handles the supply problems.

    I believe a guaranteed solution would be to get a “Continuous” UPS to run the computers, that way you are running the computers through an inverter from the battery giving a clean sine wave with a good voltage.

    I hope this makes sense.
     
  5. HandySparks
    Offline

    HandySparks Forum Mentor

    Location:
    Hampshire
    Business Name:
    Neish Electrical Services
    Fitting a UPS feels to me like the wrong fix.

    I'd check R1, R2 and Rn for the circuit and measure Zs and the supply impedance (like Zs, but L to N). Also check whether there's some other noisy load on the circuit which might affect the computers. After that I'd get a like for like replacement for the PSUs in case there's a faulty batch. If the PSUs and computers can't work with a normal UK supply, there's something wrong with them.
     
    • Agree Agree x 2
  6. Strima
    Offline

    Strima Electrician's Arms

    Location:
    St Neots
    What's the earthing arrangement on the circuit? Is it a high integrity circuit?
     
  7. Davisonp
    Offline

    Davisonp Regular EF Member

    Location:
    Amersham
    Business Name:
    Absolutely All Electrical LTD
    Fitting a UPS feels to me like the wrong fix.

    Yes, but I cannot think of an alternative.

    I'd check R1, R2 and Rn for the circuit and measure Zs and the supply impedance (like Zs, but L to N).

    Zs about 0.43Ω Live to neutral loop 0.35

    Also check whether there's some other noisy load on the circuit which might affect the computers.

    I don’t know where to start with that.

    After that I'd get a like for like replacement for the PSUs in case there's a faulty batch.

    Tried that today. Replaced unregulated transformer with completely different brand of transformer with regulated output and got exactly the same results. Also, these transformers work in other parts of the building.

    If the PSUs and computers can't work with a normal UK supply, there's something wrong with them.

    I agree, however, when a high quality independent regulated output transformer makes no difference, it implies something happening in the mains coming into the room.
     
  8. Davisonp
    Offline

    Davisonp Regular EF Member

    Location:
    Amersham
    Business Name:
    Absolutely All Electrical LTD
    The building is TNC-S and yesterday I converted one ring to a high integrity earth setup including splitting the earth at the distribution board with no improvement.

    I do struggle to understand how the earthing system could affect unearthed equipment?
     
  9. Strima
    Offline

    Strima Electrician's Arms

    Location:
    St Neots
    Switched mode power supplies and the like require a good earth as the rectifier capacitors like to dump to earth. A poor earth and the PSU won't run properly.

    Just out of curiosity is the CPC the same CSA as the conductors?

    Have you tried just running one PSU on the circuit? Is there anything else connected such as printer, photocopier etc?
     
    • Like Like x 2
    • Informative Informative x 1
  10. Davisonp
    Offline

    Davisonp Regular EF Member

    Location:
    Amersham
    Business Name:
    Absolutely All Electrical LTD
    There are three separate rings in three offices all next to each other. The earth is 1.5mm.
    I converted one ring with 8 sockets into a high integrity earthed ring.
    On this ring, there are only three sockets in use. One with an extension lead with 6 things plugged in. There are 4 computers and 4 screens, and one Samsung phone charger.
    Since the problem occurs in all three offices, it appears to be either a problem from outside, or that the computers are particularly vulnerable to interference (which is what I suspect) as no other computers in the building have this issue, only the new ones in the three offices, not the old ones that have been replaced.
     
    • Like Like x 2
  11. Strima
    Offline

    Strima Electrician's Arms

    Location:
    St Neots
    Very strange, I'm a bit stumped at the minute.
     
    • Like Like x 1
  12. Davisonp
    Offline

    Davisonp Regular EF Member

    Location:
    Amersham
    Business Name:
    Absolutely All Electrical LTD
    Yes, I am stumped too.

    I forgot to mention that the computers were replaced a short while ago, and the new computers had this issue immediately and ever since, but the old computers of various manufactures never had an issue.

    I think there is a slight dirty electricity issue in the building, but that the new computers are over sensitive to this but the bosses want the issue solved and the computer company are blaming the supply.
     
    • Like Like x 1
  13. Strima
    Offline

    Strima Electrician's Arms

    Location:
    St Neots
    The computer company would blame the supply. What make of PSU are they?
     
    • Agree Agree x 1
  14. DPG
    Offline

    DPG Respected Member

    Location:
    S Yorkshire
    Wouldn't cost much to get a small UPS to try with one of the computers - would give you more to go on then.
     
    • Like Like x 1
  15. Pete999
    Online

    Pete999 Forum Mentor

    Location:
    Northampton
    Business Name:
    None
    Judging from your responses, you haven't even entertained my suggestions, just plumped for the UPs syndrome, which isn't going to provide you with what you want
    My suggestion would be rather than hoping to find the answer to your problem, from well meaning and informed replies, you may do better by laying out the exact problem and what you have/are doing about it and go to a reputable power supply company, explaining your concerns, asking for a site visit, so they can see first hand the environment and working conditions, you may be pleasantly surprised by the responses.
    Dduring my time as Head of of the electrical section where I worked I found most firms would visit FOC to offer their equipment as a remedy for your problems, could save you or your company a lot of unnecessary time and money.
     
    • Like Like x 2
Loading...
Similar Threads - Recomendations Power Supply Forum Date
Domestic Changed socket but still no power Electrical Forum Saturday at 11:22 AM
What power rating would this garage door be? Electrical Forum Feb 9, 2019
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job