bear in mind that not all loads will be in use simultaneously. applying diversity, I'd allow for an aveage load of 8kW. that equates to c. 40A, so as far as current capacity, 16mm will,be fine. volt drop however may be a factor.

Thank you everyone for your advice.

The reason I put my post was that I had two conflicting quotes from local electricians.

One said that my existing 16mm armoured cable would be OK and quoted me £480 to upgrade my outdated fuse box with a new consumer unit including safety certificate.

The other said that 16mm would be unsafe and a fire risk and quoted me £6900 to replace with 25mm armoured cable.

Will my 16mm cable by unsafe and a fire risk, or just a voltage drop that will mean I might have to replace my existing fluorescent fittings?
 
Thank you everyone for your advice.

The reason I put my post was that I had two conflicting quotes from local electricians.

One said that my existing 16mm armoured cable would be OK and quoted me £480 to upgrade my outdated fuse box with a new consumer unit including safety certificate.

The other said that 16mm would be unsafe and a fire risk and quoted me £6900 to replace with 25mm armoured cable.

Will my 16mm cable by unsafe and a fire risk, or just a voltage drop that will mean I might have to replace my existing fluorescent fittings?

What size circuit breaker/fuse did the electricians quote, for this circuit?
 
Hi - 16mm SWA buried is good for 78A single phase, which is about 18kW load. Your loads add up to less than this so in my humble opinion it's not the 16mm that might be a fire hazard. (It might be something else he's spotted?). Certainly there would be a significant voltage drop over 100m.
 
The quote wasn't detailed and did not say.

Ok.
As mentioned above, if you want to use the existing 16mm cable then the max size breaker/fuse you can have is 25A. Anything bigger and you will exceed the 3% voltage drop for your lighting.
 
If you are using the office for yourself and are concious on what you are using together then the 16mm on a 25A MCB should be ok. Must be a big shed for that many heaters?

I would go with the upgrade however and get a fully detailed quote before placing the order.
 
I would be using a fuse at source otherwise it could be a long walk when something trips out.
 
I am not an electrician. Can any
You're obviously in possession of warm clothing.
I get 23.91 Amperes with just the heaters on full balls.
i could not be arsed to work out the VD as books are in van. however, for wtat it would cost to replace the 16mm cable versus exceeding the 3% for lighting, I'd fit LED lights which are happy with a slightly reduced voltage and sod it. at the end if the day, it's only a shed, not a hospital operating theatre. tin hat ready.

one help please?

I have an outbuilding which I am converting into two offices.

The building is currently served by a 16mm armoured cable running underground from my house, the distance is about 100 metres.

Potentially the building could have a maximum of the following appliances:-

2x2kw electric oil filled radiators
1x1.5kw electric oil filled radiator
Hand wash 2.5kw
Electric Kettle 2.5kw
Saniflo 400 watts
Vacuum Cleaner 1kw
4 Fluorescent Lights
2 Computers
Total aprox 13kw

Will the existing 16mm cable be adequate or will I have to have it replaced with a 25mm armoured cable.

Thank you
 

Reply to Armoured cable 16mm or 25mm in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock