Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Discuss Aurora 3.0 inverter on a 3.84kw system - is this reasonable? in the Solar PV Forum area at ElectrciansForums.co.uk.

Thread Status:
Not open for further replies.
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. upnorth01
    Offline

    upnorth01 Guest

    I had a solar panel installation completed this week. There are 16 x Csun 240-60P panels (3.84kw capacity, on a SW facing roof in north-east Scotland) and a power-one Aurora PVI-3.0-OUTD inverter. From the inverter booklet I see this has a max recommended DC power in of 3.5kw and max AC power out of 3.3kw. It seems from my reading of the sepcification that this is too small a unit and the system should have been fitted with a PVI-3.6 model. I guess I have 3 questions - is this system within a reasonable tolerance or does the inverter need to be changed, what will happen when the panels deliver more power than the inverter can cope with (damage the inverter / output stops altogether / output continues subject to the maximum cap of what the inverter can process etc) and will running near full capacity reduce the life of the inverter.

    Any help or comments will be appreciated. I have found the forum most helpful. Thank you.
     
    Last edited by a moderator: Feb 26, 2012
  2. BruceB
    Offline

    BruceB Electrician's Arms

    Location:
    Bath/Bristol
    Re: Aurora 3.0 inverter on a 3.68kw system - is this reasonable?

    16 x 240 = 3840. Are you sure it is 3.68?

    - The inverter is undersized. The correct Aurora model would be the PVI-3.6-OUTD (use the UK version limited to 16A).
    - The inverter will only draw from the panels what it can deal with so no damage will be done provided the string(s) have been wired so that input voltages are within tolerance.
    - Running at full power all the time will reduce the life of the inverter.
    - You will lose some of the annual production because of limiting.
     
  3. upnorth01
    Offline

    upnorth01 Guest

    Bruce,

    Oops - indeed it is 3.84 - got the figures mixed - edited my post to correct. Thank you for the information - its not as bad as I feared (not dangerous and production continues rather than just stops) but I will try and persuade the installer to replace. I suspect this will be met with some opposition. Would MCS take up a case like this, and if so is it likely to yield any results?
     
    Last edited by a moderator: Feb 26, 2012
  4. BruceB
    Offline

    BruceB Electrician's Arms

    Location:
    Bath/Bristol
    Re: Aurora 3.0 inverter on a 3.86kw system - is this reasonable?

    3.84

    It is a pretty clear mistake if all is as you have presented it and the installer should be willing to fix it. You will have to go through their complaints process before any of the supervising bodies will get involved.
     
Loading...
Similar Threads - Aurora inverter 84kw Forum Date
single to 3 phase inverter Electrical Forum Feb 5, 2019
Inverters for 150 kWp Photovoltaic Solar PV Forum Jan 31, 2019
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job