hi all

just wondering if any of you know anything about auto power correction? the reason i am asking is i have several 100amp single phase installations that are running at full capacity, so i was wondering if power correction would reduce the full load current? therefore reducing running costs? probably 80 - 90 amps of that are motors and maybe 5 - 10 amps are fluorescent lighting which do have pf capacitors fitted as standard. if any one has any info it will be greatly appreciated as i have no real experience in this field.

regards
gary
 
How are these supplies metered?
Most 100A supplies are on KW/h meters so you wouldn't make any savings.
 
The current, voltage and power factor at the motor terminals do not change. The current and power factor between the capacitors and the supply are affected by the addition of the capacitors. The power drawn by the motor does not change. In effect, the capacitors are supplying some of the magnetising current of the motor, instead of it coming from the supply.
 
If we base the loading as purely inductive 100A @415V = 60KW @ .8PF
Adding 30KVAr of capacitors will lower the current to 87A @415V = 60KW @.95PF. It still equals 60KW that you will have to pay for.
You need to determine the loading of the motors on you system. The PF correction can not be switched in en-mass but needs to come in in stages. Otherwise you will have over correction
To be honest you should look at having your supply up rated and forget PF correction. There’s no financial gain from it with KWHr meters. If you were on KVA meters there would be.
If your thinking of lowering the line current by PF correction so you can add more load then I think your heading down a dangerous road.
 
Last edited by a moderator:
What are the ratings of capacitors needed to a)correct pf b)reduce starting current of 1ph/3ph induction motors of different hp/rpm.Can someone give a link?.Thanks
 
thanks for your replies

i thought it wouldnt be that simple, you are right upgrading supply would be the best solution, but the cost can be huge. so i was iust wondering could power correction be used.

many thanks
gary
 

Reply to automatic power correction panel in the Canada area at ElectriciansForums.net

Similar Threads

Cathodic Protection Station with Switching Power Supply for Buried Metal Structures Benefits of the Switchmode Cathodic Protection Rectifier...
Replies
1
Views
463
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
0
Views
560
I have hooked up a 30 amp interlock switch to my main panel run off my generator. However, only my light switches work none of my plug-ins have...
Replies
10
Views
722
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock