832FF578-885E-428F-B213-E0FD0CAD6FFE.jpeg Had a callout for a landlord as the bathroom fan stopped working.

Didnt take too long to work out why...

Never seen a fan quite as bad as this before!!

Wonder what caused this, possibly got jammed and overheated?
 
The 3A fuse is not there to prevent what happened in the OPs pic but to prevent fire, it will always get to that stage in the pic. I know some university carried out some trials with this and the results were hit and miss between not only the manufacturer of the extractor but also the fuse brand.
 
An appropriately sized fuse designed for use in appliances and built in to the fan would stand a far better chance of preventing fire than a 3A plug fuse
Agreed but when you can get an extractor for two bob and three Woodbines it is not going to happen.
 
This is what happens when an 'impedance protected' shaded pole motor is pad mounted in a cheap plastic frame and it suffers a locked rotor condition. The jammed blade means there's no air over the motor to cool it plus the higher LRA means more heat as well. The plastic mounts weren't capable of handling the heat. Not sure it was actually a fire risk because I doubt it would have reached flash point temperature but certainly poorly constructed and designed.
 
This is what happens when an 'impedance protected' shaded pole motor is pad mounted in a cheap plastic frame and it suffers a locked rotor condition. The jammed blade means there's no air over the motor to cool it plus the higher LRA means more heat as well. The plastic mounts weren't capable of handling the heat. Not sure it was actually a fire risk because I doubt it would have reached flash point temperature but certainly poorly constructed and designed.
Interesting, do you think ZP is considered with the construction of a chuck away extract fan.
 
I always fit 3A fuses in fan isolators using click mode modules..If it had started a fire and gone to court the MI would say it states MUST be protected by 3amp fuse if the contractor hasnot followed these then responsibility could be past to the contractor. For the sake of £1 just i fit it!
How about holding the manfacturers responsible for not providing something fit for purpose? Unless its connected to a socket circuit then there should be no need to fuse it down, you dont after all fuse down all individual light fittings do you?
 
Depending on ambient temperatures impedance protected motors of < 100 watts will generally reach up to 150 degrees Celsius if they're locked rotor for an extended period. That's hot enough for mountings to distort badly if they're PVC but not hot enough to cause much discolouration of the windings.

Interesting, do you think ZP is considered with the construction of a chuck away extract fan.
A lot of very small motors are designed and classed as ZP (impedance protected). ZP open frame shaded pole motors like this one are common, also a lot of computer type fan motors are also rated as ZP.
 
How about holding the manfacturers responsible for not providing something fit for purpose? Unless its connected to a socket circuit then there should be no need to fuse it down, you dont after all fuse down all individual light fittings do you?

Light fittings do not stipulate being fed off a 3A fuse through a double pole isolator, i dont see light fittings as much of a threat to going on fire as a motor inside a fan. I agree the manufacturers should do more,,but in mean time cover your own derrière..
 

Reply to Bathroom fan burnt out..... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I currently have two switches in my bathroom. One controls the lights above the sink and the other controls a light above the toilet and...
Replies
0
Views
731
HI There, I would be grateful if you could help me, I have a very long duct between the bathroom and extractor outlet vent and for sometime, the...
Replies
3
Views
982
We are having issues with our electrical system. In the garage, dining room, kitchen, one of two bathrooms, master bedroom and the front yard...
Replies
5
Views
691
Hi All, Bit of a tricky number. I have recently installed lights / fans /toothbrush chargers and shaver sockets to a bathroom and En-suite. The...
Replies
6
Views
1K
Hello I have an old timed extractor fan in the bathroom which has stopped working. It has 3 wires which are black, brown and grey. I believe that...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock