Discuss Bit confused in the UK Electrical Forum area at ElectriciansForums.net

R

Rich306

I'm currently doing the 2357 City and Guilds coursework at this precise moment, but i cannot seem to get my head round what should be a simple process in the design area.
Hopefully you guys will be willing to help me get round this first question so i can understand and complete the remaining questions.
Its regarding the minimum size CPC for 'each circuits' (one only provided).
I need to give consideration to disconnection times and thermal constraints.
Here is the details i have so far.

Prospective fault current - 50 kA -(doesn't seem right)?
400v Supply three phase
Ze of 0.008
i need to work out the CPC size for a 5kW 400v 3 phase machine.

I've looked in the Wiring regs and even looked at the adiabatic equation but still cannot get my head around it.
I know the following:

S is the nominal CSA of the conductor in mm[SUP]2[/SUP]
I is the value in amperes of fault current
t is the operating time of the disconnecting time in seconds. (But would that be type C circuit breaker? and what sort of time would i need to give for the above circuit?? 0.1 or 5?)
k being the factor of resistivity and temperature of the material.


A walk through talk through would be appreciated?

Thanks in advance.
 
What type of protective device had been given?

I had to choose the protective device.

These are the calculations i had made a while back relating to this machine
i). 5kW, 400V three-phase machine
*Design current = 12.5A
*Overcurrent device = 16A
*Wiring enclosed in Metallic trunking
*Ambient temperature of 25degrees C
*Tabulated current = 23.98A
*Size Cable required = 4mm[SUP]2[/SUP]
*Length of cable required –19.4m
*Voltage drop = 2.3V
 
I had to choose the protective device.

These are the calculations i had made a while back relating to this machine
i). 5kW, 400V three-phase machine
*Design current = 12.5A
*Overcurrent device = 16A
*Wiring enclosed in Metallic trunking
*Ambient temperature of 25degrees C
*Tabulated current = 23.98A
*Size Cable required = 4mm[SUP]2[/SUP]
*Length of cable required –19.4m
*Voltage drop = 2.3V

You might want to re-check your previous calculations, the bits highlighted in red first.
 
Depends on how you calculate it,

kW / (Line Voltage X root 3)

or (kW / line voltage) / root 3

When you are given the kW value initially, it simplifies the calculation somewhat,as the PF and EF is already taken care of in the final kW value.

It is not as simple working the calculation forward. for where a motor/machine is involved then: Power (Watts) = 1.73 × Line Volts × Line Amps × PF × Efficiency.


Calculate it again, you are nearer.
 

Reply to Bit confused in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Replies
9
Views
1K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
844

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock