Discuss Blanks missing from CU in 2 senarios in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

1 - C2
2 - C1
3 - C3 if all plastic, C2 if any metal.
Sorry, should have mentioned the CSA of the conductors for the lights on the stairs is 2.5mm2.
Obviously 3 was a C2 as the face plate was live.

During the course of my testing I de-energised and re-energised the circuits a few times.
Though I did remove the C1 first.
 
Sorry, should have mentioned the CSA of the conductors for the lights on the stairs is 2.5mm2.
Obviously 3 was a C2 as the face plate was live.

During the course of my testing I de-energised and re-energised the circuits a few times.
Though I did remove the C1 first.
What lights where fitted?
Regulation 559.5.1.204 states that B15,B22,E14 and E27 lampholders shall be protected by an OCPD of a maximum rating of 16 amps
 
Like said by another. This just goes to show how ambiguous coding can be. I beleave there is a coding course available or will be available from the NICEIC. this should at least give all NICEIC Members the chance to sing from the same song sheet . But then the problem arises when another organisation holds there own coding and this has variables from NIC.
Anyway sorry for starting this debate. All's good with the CU's now as all blanks were fitted today. As this was the first test I think the missing blanks were an after thought that was forgotten about by the original installers. Obviously they overlooked it in there original certs.
 
New posts

Reply to Blanks missing from CU in 2 senarios in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
788
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
595
Hi, I am looking to convert a 2 way light into just control by single switch. I have searched and looked for similar questions here, and found a...
Replies
4
Views
1K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
537
Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock