Posting a message to the forum will remove the above advertisement

Discuss Boiler wired from lighting circuit in the Electrical Forum area at ElectrciansForums.co.uk.

Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. concerned321
    Offline

    concerned321 New EF Member

    Location:
    grimsby
    Hello. I'm just looking for a bit of advice.

    I had a new boiler fitted a few months ago. An electrician came and wired it up and left me a Minor Electrical Installation Works certificate.

    ive just had a plumber round to check the work and he says the electrician has wired the boiler from the lighting circuit and he shouldn't have done this because it is a 6 amp switch in the fusebox.

    The electrician says it is ok because he has fitted a switch next to the boiler with a 3 amp fuse in it.

    could you tell me which one of them is right please?

    Many thanks
     
  2. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    unconventional, but not a problem. a bathroom fan is usually fitted with a 3A fuseand that's wired from the lighting.
     
    • Like Like x 1
  3. Last plumber
    Offline

    Last plumber Electrician's Arms

    Location:
    Lancashire
    As above but Just for curiosity, is that circuit on an RCD or RCBO?
     
  4. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    but does it need one? is cable buried< 50mm in wall/s?. does boiler blurb specify fitting one?
     
  5. FatAlan
    Offline

    FatAlan Trainee Trainee Access

    Location:
    Surrey
    Presumably the load on a gas boiler is pretty low due it being just switching?
     
  6. FatAlan
    Offline

    FatAlan Trainee Trainee Access

    Location:
    Surrey
    Further to the above. Presumably, if your lighting circuit tripped out you'd lose your heating at the same time.
     
  7. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    The sparky is correct!
     
  8. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    that short comment reminds me of the classic comment " the sherrif's a Ni**er".
     
    • Like Like x 3
  9. Last plumber
    Offline

    Last plumber Electrician's Arms

    Location:
    Lancashire
    Not necessarily, I'm just curious !
     
  10. Last plumber
    Offline

    Last plumber Electrician's Arms

    Location:
    Lancashire
    Normally 1 to 2 amp ish, there and there abouts( domestic )
     
    • Like Like x 1
Loading...
Similar Threads - Boiler wired lighting Forum Date
Fitting Hive 2 to a oil boiler in Spain Non UK Electrical Works Aug 2, 2017
Nest wiring for combi boiler Electrical Forum Jul 12, 2017

Share This Page

  • Electricians Directory Post a Domestic Job Post a Commercial Job