The trouble is not knowing the earthing arrangments, the example I gave in a fault condition like losing PME neutral main house you would be introducing a different potential TT back from the flat therefore the equpotential zone in the house now has potential earth, and bonding would not stop the risk of electric shook in the house.
 
Okay so what if you walked through the front door of the granny flat and had no access to next door... You found NO BONDING so tested to see if the water pipe was extraneous and found that it was not? we'd stick a bond on it anyway??? This then takes us to the long debate that has been battled out in other threads which makes out you should bond metal windows and loose change on the bedside cabinets etc (Engineer54 will remember that one I'm sure);)

If it's bonded next door and that's the reason you get your test results then you won't know that BUT the bonding next door will have a clamp attaching it to a pipe which will also have a label on it saying "Electrical Earth Connection - DO NOT REMOVE"!

If you've bonded the pipework and then the supply pipe is replaced with a plastic one then you have now created a potentially lethal situation if a fault were to occur.

You cannot be accountable for what a wet head decides to do or not do when he goes in after you?

A block of flats is entirely different and as I recently was informed each one AND the main installation should ALL have their own bonding (Main installation to within 600mm of stop tap and flats to within 600mm of point of entry - Where reasonably practicable)

This is my opinion based on a lot less experience than many others that have posted the opposite in this thread but to me it makes sense. I'll stand corrected though if someone can PROVE without doubt that my actions would have the book thrown at me in a court of law.

:thumbsup
 
a clamp attaching it to a pipe which will also have a label on it saying "Electrical Earth Connection - DO NOT REMOVE"!

My mistake, it actually says " Electrical Safety Connection - DO NOT REMOVE" :thumbsup

Better squeeze that in before I get picked up on it :D
 

Reply to bonding conundrum in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
Replies
9
Views
507
Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
835
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock