I'm aware that a 10mm earth cable needs to run to the incoming water and gas supply but I was wondering if someone could tell me whether this should be from the consumer unit, the main incoming fuse, or both? TIA
 
bonding should be to the MET. this may be the strip in the CU or external. then main earth conductor to head if pme.
 
I'm aware that a 10mm earth cable needs to run to the incoming water and gas supply but I was wondering if someone could tell me whether this should be from the consumer unit, the main incoming fuse, or both? TIA
There are some videos/articles that suggest that distances between the MET and the point of entry of Gas and Water then the Main bonding conductor should be increased to 16mm2, this is a suggestion from people more in tune with this subject than myself, just passing on some information I have heard and seen.
Like I said if you don't agree, then don't blame the delivery Boy please.
 
There are some videos/articles that suggest that distances between the MET and the point of entry of Gas and Water then the Main bonding conductor should be increased to 16mm2, this is a suggestion from people more in tune with this subject than myself, just passing on some information I have heard and seen.
For your information and assimilation.
 
There are some videos/articles that suggest that distances between the MET and the point of entry of Gas and Water then the Main bonding conductor should be increased to 16mm2
They are incorrect. Nowhere does BS7671 state or in any way imply that there is a 0.05 Ohm limit to a main protective bonding conductor. This measurement is intended to prove that the connection between the main protective bonding conductor and the extraneous-conductive-part is effectively made. It has absolutely nothing to do with conductor resistance.
 
They are incorrect. Nowhere does BS7671 state or in any way imply that there is a 0.05 Ohm limit to a main protective bonding conductor. This measurement is intended to prove that the connection between the main protective bonding conductor and the extraneous-conductive-part is effectively made. It has absolutely nothing to do with conductor resistance.
Funny you should bring this up did the 18th Ed update yesterday and the tutor mentioned this figure and I asked where it was stated in the Regs which drew a blank look.
 
There is a calculation in the book based on the size of the largest protective device for bonding, I can't for the life of me remember where it is. I'll have a look for it later.
 
Funny you should bring this up did the 18th Ed update yesterday and the tutor mentioned this figure and I asked where it was stated in the Regs which drew a blank look.

It's mentioned a couple or maybe three times in GN3 that I know of. None of the mentions relates to the resistance of the entire conductor along its length, although this an almost universally held belief.
 
They are incorrect. Nowhere does BS7671 state or in any way imply that there is a 0.05 Ohm limit to a main protective bonding conductor. This measurement is intended to prove that the connection between the main protective bonding conductor and the extraneous-conductive-part is effectively made. It has absolutely nothing to do with conductor resistance.
So sick of hearing this rubbish especially from the apprentices we have at our company being taught false information from tutors
 
It’s not the adiabatic. This is specifically for bonding conductors not CPCs.
Yeah, 544.1.1
Except where PME applies, Main Protective Bonding Conductors shall not be less than half the csa of Earthing Conductor. You use selection or the adiabatic to size your earthing conductor......and then size bonding conductor from that, but not less than 6mm csa.
 

Reply to Bonding - CU or Main Incoming Fuse in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Incoming supply on our job comes into the building and then the tails from which go into a switched isolator with 200A fuses fitted. No idea...
Replies
5
Views
951
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
Been asked to do some rewiring, and have said needs upgrade of consumer unit really Main question is regarding earthing - Zs reads at 0.45 ohms...
Replies
7
Views
1K
Hi I have a domestic installation to rewire and the main incoming fuse is 80 amp so i am using 16mm double insulated tails, is the main earth size...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock