If you cannot prove it isn’t then yes.

Turn it on it’s head, would it be correct not to?

Ah but you originally (#17) said it's sometimes easier to bond it than to prove it, implying that you wouldn't bother testing.
 
No, I was trying to imply that you can spend an age trying to prove isn’t and it can be quicker just to do it.
 
I think you will find that it says "if the water / gas pipe enters the house is of plastic construction, and the rest of the pipework is copper, then this copper must be bonded, are we not getting our wires crossed with the > than 22Kohms refers to supplementary bonding, not main bonding, open for discussion?
no.the 22k ohms is to prove whether or not a piece of copper /metal pipe is extraneous or not.
 
no.the 22k ohms is to prove whether or not a piece of copper /metal pipe is extraneous or not.
Agree but is also used to prove that something is "extraneous" the pipework should be main bonded, but not bonded because it may be or maybe not classed as extraneous.
 

Attachments

  • earthbonding.pdf
    94.1 KB · Views: 12
Last edited:
I do find reg. 544.1.2 a bit confusing therefore, i.e. if the service is plastic the continuing internal metal does not need bonding argument? Or is the reg poorly worded and not drawing reference to extraneous or not.
 
On the other thread
Equipotential Bonding Explanation - https://www.electriciansforums.co.uk/threads/equipotential-bonding-explanation.136192/
if the metal pipework is not bonded, because the incoming service is plastic, when the kettle casing becomes live, the pipework may be not at the same PD, but could be earthed via parallel paths, so at the moment of the fault 'the touch voltage that may be experienced during a fault, i.e. for the 0.4s before the automatic disconnection occurs' (mentioned by RB) may be increased?
 
So is this topic a grey area in general lol I can never find or hear a straight answer for it as I have also heard that bonding something that doesn’t need a bond will possibly start a not needed potential??
 
It's not a grey area. If it's an extraneous conductive part it needs bonding. If it's not an extraneous conductive part it doesn't need bonding. I always run a green and yellow in for gas and water on a new builds as I've had muppet meter fitters refusing to connect as no bonding, even though it didn't require bonding. If they moan I connect it then chop it off when the muppet has finished.
 
Must admit, I'm still confusing myself over this. I understand the testing to conclude if a metal pipework after a plastic service is extraneous or not.

I take spinlondons point that bonding the above, under fault conditions may momentarily 'increase the number of conductive parts that will become live', but wouldn't these be earthed anyway by a circuit cpc?

The OSG recommends bonding of above, unless its been confirmed said pipework is not introducing Earth potential. It mentions pipework 'liable to introduce earth potential'. It doesn't mention testing to prove whether such pipes are extraneous, only gives examples, as in reg 411.3.1.2. Indeed the formulae for when doubt exists over effectiveness of extraneous or not, reg 415.2.2 is for supplementary bonding, something completely different. Reg 544.1.2 states where the consumers hard metal pipework should be bonded after insulating section or insert.

So I'm suggesting BS7671 recommends that unless you can physically confirm all such pipework is not liable to or not able to, then it should be bonded?
 
I don’t bother with the OSGs, as they contain so many errors.

Are you stating that the OSGs recommend bonding non-extraneous conductive-parts?

But it does contain some pretty pictures for us plebs. :)

Have a shufty yourself, it talks about it on pages 44 & 46 in the yellow version.
 
But it does contain some pretty pictures for us plebs. :)

Have a shufty yourself, it talks about it on pages 44 & 46 in the yellow version.
Unfortunately, that is not possible.
I only have a brown 16th and a red 17th someone gave me.
My point is however, BS7671 requires protective bonding for extraneous conductive-parts, not for non-extraneous conductive-parts.
 
Unfortunately, that is not possible.
I only have a brown 16th and a red 17th someone gave me.
My point is however, BS7671 requires protective bonding for extraneous conductive-parts, not for non-extraneous conductive-parts.

Oohh ok, give me 5 mins, I'll type up what the OSG says. Might be 10, just sipping a G&T :)
 
Yellow OSG Sec 4.5 'Main protective bonding of plastic services'. There's no shock here (excuse the pun), it says there's no requirement to bond plastic services.

Continuing on page 46; 'Where there is a plastic service and a metal installation within the premises, main bonding is recommended unless it has been confirmed that any metallic pipework within the building is not introducing Earth potential (see 4.3, (referencing to reg 411.3.1.2).

I have had a quick shufty through GN8, and can't seem to find specific mention of the above scenario.

What do you make of the definition of extraneous-conductive-part in BS7671?
 
It goes onto say about internal metallic pipework which may be buried in the ground for convenience............but I'm not typing all that out for you :)
 

Reply to Bonding gas/water yellow and blue in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
407
I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be...
Replies
14
Views
2K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
In a job today me and my colleague where discussing whether or not we had to earth the incoming water. It comes in blue pipe as you can see from...
Replies
15
Views
4K
Good afternoon one and all. I, like many non-electricians are having issues regarding the need to have domestic water pipes (plastic entry to the...
Replies
4
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock