Can someone reference the reg for testing an extraneous-conductive-part, in the examples given by 411.3.1.2. I only ask that, you would not need to test (those examples), as the reg says they have to be bonded, end of?
There’s no Reg stating you have to test whether something is an extraneous conductive-Part.
There’s no need for one.
If it’s extraneous (i.e. comes into the building from outside), is conductive (i.e. can conduct electricity) and likely to introduce a difference in potential, then it needs bonding.

Determining whether something is extraneous is relatively easy, in the majority of instances you don’t even need to look, you just know.
Gas, water, electricity, cable TV, satalite TV, waste water, telephone, oil, etc. they’re all extraneous.

Determining whether something is a conductive-part however, seems to be problematic.
Plastic coated telephone cables, satellite and cable TV cables along with plastic waste pipes are all deemed as non-conductive.
For some reason, there’s confusion as to whether plastic gas pipes, plastic water pipes and plastic coated oil lines are conductive.
Because of this confusion, a lot of people are advising we test these supplies to determine whether there’s any connection to Earth.
Unfortunately there seems to be various views on what resistances indicate either a reliable connection to Earth or no connection to Earth.
Some say 0.05 Ohms, others say 20 Ohms indicate a reliable connection to Earth.
For whether there’s no connection to Earth the figures for resistance are 23 Mohms or 7.67 Kohms (22 Mohms and 6.67 Kohms when the 1 Mohm resistance of the human body is taken into account).
 
There’s no Reg stating you have to test whether something is an extraneous conductive-Part.
There’s no need for one.
If it’s extraneous (i.e. comes into the building from outside), is conductive (i.e. can conduct electricity) and likely to introduce a difference in potential, then it needs bonding.

Determining whether something is extraneous is relatively easy, in the majority of instances you don’t even need to look, you just know.
Gas, water, electricity, cable TV, satalite TV, waste water, telephone, oil, etc. they’re all extraneous.

Tis what I've been saying for the best part of this thread. If its metal and comes out of the ground or into a building, then according to 411.3.1.2 it needs bonding. Some are suggesting testing it. Doesn't need testing, just bonding.

My rub is, with the plastic metal combo, unless your building the property yourself, how do you ensure that the metal part of the combo, isn't 'liable' to do the above.
 
I did some students flats last year.
Plastic incoming water supply to each building then copper pipework.
From copper in the corridors it went to plastic entering each student room.
Showed the apprentice the testing procedure for testing extraneous parts using an insulation resistance tester.
The result was around 20Mohms.
Did I bond any copper pipes?
NOPE!:)
 
Ok my last swipe at this; you don't test the pipes for 411.3.1.2, 544.1.2 says bond it after plastic.

I think this will just keep going around, until the 18th comes out.

This had an interesting discussion on such testing etc;

Bonding water services when plastic pipes are present - https://www.electriciansforums.co.uk/threads/bonding-water-services-when-plastic-pipes-are-present.61592/

Earthing water. Part plastic, part copper - https://www.electriciansforums.co.uk/threads/earthing-water-part-plastic-part-copper.30881/
 
re spinlondon's post:

The other problem is that the minimum CSA for an Earth conductor buried in the ground and not protected against corrosion by a sheath is 25mm2, 16mm2 if protected.

sureley that's for an earthing conductor, as in connected to a rod., not for a bonding conductor?
Alsways took it as applying to al Earth conductors.
Main earths, bonding, CPCs, etc.
 
Still not convinced.

However, having verified (by testing) that the internal metal pipework was extraneous and required bonding, would you bond it using a main protective bonding conductor or using a supplementary bonding conductor?
 
It's not a grey area. If it's an extraneous conductive part it needs bonding. If it's not an extraneous conductive part it doesn't need bonding. I always run a green and yellow in for gas and water on a new builds as I've had muppet meter fitters refusing to connect as no bonding, even though it didn't require bonding. If they moan I connect it then chop it off when the muppet has finished.

The other favourite of theirs is when they tell you the gas isn't bonded and they've only looked at the external meter box. They then insist it should be bonded at the external meter box even though we all know the regs say it should be at the point of entry into the building. Muppets
 
The other favourite of theirs is when they tell you the gas isn't bonded and they've only looked at the external meter box. They then insist it should be bonded at the external meter box even though we all know the regs say it should be at the point of entry into the building. Muppets
Lets be fair the meter box IS the entry point to the building, albeit external, that's where the Gas and Electricity enter the building, it does in my house.
 
Let’s face it if you didn’t bond it at the meter box then the only other logical place is the likes of the boiler as take new builds the pipe enters the house and is buried in the wall.
Then it’s not bonded within 600mm of point of entry.
 

Reply to Bonding gas/water yellow and blue in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be...
Replies
14
Views
2K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
In a job today me and my colleague where discussing whether or not we had to earth the incoming water. It comes in blue pipe as you can see from...
Replies
15
Views
4K
Good afternoon one and all. I, like many non-electricians are having issues regarding the need to have domestic water pipes (plastic entry to the...
Replies
4
Views
5K
Hi guys Does the earth Bonding HAVE to be done at the meter or can it be put on the gas inlet to the boiler in a utility room? Plans have changed...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock