The external earth potential that is being introduced into the property will come from the gas supply pipe which is bonded at the point of entry, this covers the bonding requirements; otherwise you would need to bond the gas pipe every few centimetres because it is connected to another bit of metal just before it that is introducing earth potential and so on. The water pipes are not introducing a new earth potential they are just extending the area over which the already bonded service spreads.Even with a plastic incoming water supply, if the installation is completely metallic (copper) it will almost definitely be introducing earth potential via the connection at the boiler. Where the plumber has bonded all the pipes together at the boiler as in the above picture, you can be sure all the metallic pipework will be introducing earth potential as the gas supply pipe to the boiler will be metallic and earthed at the boiler.
So unless you can confirm the pipework is not at earth potential (which it will be if it is an all metallic installation and the boiler supply is correctly earthed) then it will need bonding.
On a minor electrical installation works certificate you sign to say that the safety of the installation has not been impaired by your work.Well I can’t see how say you move a light switch from one wall to another and you complete a minor works certificate PME earthing arrangement.
If the main protective bonding is in 6mm and has been there say all the installations life maybe 30 years, then to say you have to upgrade to 10mm which could be a pig of a job is ridiculous in my opinion
This implies that there is no requirement to enhance the safety of the installation to the current regulations despite the requirement that earthing and bonding is adequate for the protective measure applied.