Bit of a debate today, advice please as regs book not possible to get in my hands until tomorrow. New job, apartments, in the kitchen there are 2 x 25mm conduits from an external wall to an island within the kitchen that is free standing, to be able to get the hob supply across and lighting with a spare in case any sockets are added at a later date. My question is, do these require bonding? Thanks in advance.
 
If they are in good contact with earth(generally below the foundations) and meet the definition of an extraneous conductive part then They will require protective bonding to the MET
 
Bit of a debate today, advice please as regs book not possible to get in my hands until tomorrow. New job, apartments, in the kitchen there are 2 x 25mm conduits from an external wall to an island within the kitchen that is free standing, to be able to get the hob supply across and lighting with a spare in case any sockets are added at a later date. My question is, do these require bonding? Thanks in advance.
Have you tested the conduits to see if they are extraneous?
 
If the cable installed inside the conduit is insulated and sheathed such as twin&earth , then does it still need to be earthed as you effectively have double insulation unlike singles?
 
Insulated and sheathed is not the same as double insulation.
No it’s not but do you see were I’m coming from?
The added protection you have with twin & earth is it necessarily needed to earth the conduit?
Perhaps if buried in the floor against impact yes but otherwise I’m not convinced.
Open to discussion
 
Try regulation 412.1.1 double or reinforced insulation
Basic protection and fault protection are provided by reinforced insulation between live parts and accessible parts.
Regulation 412.2.

Singles don’t have reinforced insulation so understandably need containment as per regulation 521.10.1,where as twin and earth does, so I’d say it’s not necessarily a requirement to Earth the conduit if metal containing insulated and sheathed cables
 
Last edited:

Reply to Bonding of conduit in kitchen floor in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock