Discuss Bonding to gas and 544.1.2 in the Electrical Forum area at ElectrciansForums.co.uk.

Tags:
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    Called today as client wanted boiler serviced/fixed. Gas safe man looked at meter boxed outside and said "No bonding! No fix!" Called me to assess. So...Clearly bonding x 2 are leaving the CU. Correct size. Test to water and Gas outside and readings below/within 0.05 ohms continuity. Suggesting there was indeed bonding connected as a previous electrician had confirmed the same. My consideration is looking at the above reg it says ...or at the point of entry to the building... Now how do you read that? Does it mean
    A: the external point of entry
    B: the internal point of entry
    I have always assumed it is a matter of where it enters the building inside. Therefore, as in this case the bonding is probably connected under the floorboards inside the front living room as readings do indicate, and evidence of bonding cables leaving CU. What is your view?
    Anyway it is clear that we must provide bonding to the outside gas meter so that work can go ahead and satisfy the gas man. Seems a bit silly to me but what else can you do.
     
  2. SparkySy
    Offline

    SparkySy Regular EF Member

    Location:
    Northamptonshire
    I have this problem too Mr gas man can't see the earth so won't touch. To be fair it should be in an accessible position for testing and inspection as it's a mechanical joint in most cases! I took the point of entry to mean where it comes in so would say internal. Also if external not in the meter box it would need some protection from the weather and the thieving types that are a magpie for copper!
     
    • Like Like x 1
    • Agree Agree x 1
  3. buzzlightyear
    Offline

    buzzlightyear still kicking sand, before pushing up daisies . Electrician's Arms

    Location:
    star command
    A out side entry .Vort . and to confrim that has been done.
     
    • Like Like x 1
    Last edited: Aug 16, 2018
  4. spinlondon
    Offline

    spinlondon Forum Mentor

    Location:
    Harlow Essex
    Can be either inside or out.
     
    • Like Like x 1
    • Agree Agree x 1
  5. buzzlightyear
    Offline

    buzzlightyear still kicking sand, before pushing up daisies . Electrician's Arms

    Location:
    star command
    if you put the bonding under the floor boards to the copper pipes there is more likely that the bonding clips might rust with moisture .
     
    • Agree Agree x 1
    • Disagree Disagree x 1
  6. Strima
    Offline

    Strima Electrician's Arms

    Location:
    St Neots
    For me the point of entry for bonding is internal however my common sense tells me that if the pipe work is not readily accessible then as close to the point of entry using suitable clamps for the environment is acceptable and within the spirit of the regulations.
     
    • Agree Agree x 4
    • Like Like x 1
  7. Dave OCD
    Offline

    Dave OCD Forum Mentor

    Location:
    Cornwall
    Business Name:
    Hendry Electrical Services
    It's more nonsense where common sense goes out of the window, I did a CU change earlier this week, it was in the attached garage. The gas pipe [28mm copper] came in to the corner of the garage then up and along the length of the garage 300mm or so above the CU. So as it was continuous and with soldered couplers/elbows I thought do I run 8 metres of 10mm back to where the pipe enters or straight up to above the CU .....
     
    • Like Like x 2
  8. spinlondon
    Offline

    spinlondon Forum Mentor

    Location:
    Harlow Essex
    I once ran a bonding cable from the CU just above the front door, into the ceiling, out through the exterior wall, up the wall into the loft, across the loft, down into the airing cupboard, through the wall into the bathroom, through some pipe boxing to the rising water main.
    All so I didn’t have to pull up the fitted carpets and floor boards.
     
    • Like Like x 2
    • Winner Winner x 1
  9. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    This is what I believe muddies the waters between GSR's and sparks!

    Gas Regs.jpg
     
    • Informative Informative x 2
    • Like Like x 1
  10. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    If the gas safe man is going on he can see the bonding at the gas meter outside so it is safe to proceed that is poor method as there is no test to ensure the bonding is intact to the MET. For all he knows it could have been cut off by the painter last year inside where you can't see it.
     
    • Agree Agree x 6
  11. KentSparky
    Offline

    KentSparky Regular EF Member

    Location:
    Kent
    This is an ongoing issue between the trades and you can spend the whole day arguing with a plumber who is trying to tell you where to place your main bond! At the end of the day electricians have their regs and plumbers have their regs,
    I was taught that you bond inside and if plums don't like it they can waste their day arguing on the phone with gas safe or niceic or whoever they choose
     
    • Like Like x 2
    • Disagree Disagree x 2
    • Agree Agree x 1
  12. buzzlightyear
    Offline

    buzzlightyear still kicking sand, before pushing up daisies . Electrician's Arms

    Location:
    star command
    what in side. new build .me don't think so . you must make a judgement on that .
     
  13. netblindpaul
    Offline

    netblindpaul Forum Mentor

    Location:
    South Wales
    Bond is to be inside the premises, some of the gas industry paperwork is simply wrong.
    It is doubtful that the gas fitter knows what is required.
    He's certainly NOT a registered Engineer, that's for sure.
     
    • Agree Agree x 1
    • Winner Winner x 1
  14. spinlondon
    Offline

    spinlondon Forum Mentor

    Location:
    Harlow Essex
    Inside back when meters were inside.
    Now it depends on where the meter is and accessibility to pipe work.
     
    • Agree Agree x 3
  15. buzzlightyear
    Offline

    buzzlightyear still kicking sand, before pushing up daisies . Electrician's Arms

    Location:
    star command
    you better tell all the sparks in uk their are doing it wrong gas out side meter .
     
    • Dumb Dumb x 1
Loading...
Similar Threads - Bonding Forum Date
EP Bonding Copper pvc copper Electrical Wiring, Theories and Regulations Dec 4, 2018
Main protective bonding/equipotential bonding Electrical Course Trainees Only Nov 30, 2018

Share This Page

Users found this page by searching for:

  1. Gas Regulations for bonding

    ,
  2. bs 544.1.2

    ,
  3. 544.1.2

Electricians Directory Post a Domestic Job Post a Commercial Job