Discuss Bonding to gas and 544.1.2 in the UK Electrical Forum area at ElectriciansForums.net

Is that the Midwest electrical services uniform fashioned by the underlings? Any chance of a photo with @Midwest in his skinny jeans and blue T?
In any case, these two chaps agree with me;

2691112.png
:)
 
The requirement is to bond extraneous conductive-parts.
Plastic is non-conductive, so doesn’t require bonding.
Metallic pipework inside the building is not extraneous, so also doesn’t require bonding.
When you look up the definition of extraneous conductive-part, it says something about not being a part of the electrical installation which may introduce a potential (might be introduce a difference in potential).
Determination of whether the pipework introduces a potential (or a difference in potential) would indicate whether it requires bonding.

I’m pretty certain this has been covered a number of times.

Use an IR tester to determine whether there is any continuity between the installation earth and the pipework and use a low ohm meter to determine whether any continuity found is reliable.

Below 0.05 ohms is considered reliably connected and doesn’t require bonding.

Anything between 0.05 ohms and 23 kohms would be considered as being in contact with earth, though there are different opinions regarding the higher end as to whether it would require bonding.

22k ohms, 1667 ohms or 667 ohms, all dependant on the resistance of an average human body (1 kohm) and the 50v considered as being safe.

Hi Spin, I realise all what you have said and agree.
Maybe I should have said if the actual gas installation is ALL metallic in nature with just the extraneously fed part being plastic. With reference to the above I just seem to recall that in that instance, and specific to gas only, that it should still be bonded. The logic behind it is, I presume, that gas appliances are more likely to have parallel paths through appliances - hobs, fires etc.
Maybe I misread a reg ages ago, and TBH I have only happened across a plastic gas feed on a few occasions. But they are obviously going to get more and more common as time goes on.
I'm going to have to get my regs book out now (on a Friday night!) to see if I can find what I read.
 
Why dont gas regs just get rid of the metal sleeve that surround the yelow plastic pipe inside to the outdide meter then making the gas service non extraneous.
I find it much easier bonding to boiler its easy to find the bond and the pipes are all crossbonded via the pipe connection plate which is handy imo.
 
In the recent NICEIC cinema show there was a part on highlighting how difficult (near on impossible) and time consuming it would be to isolate sections of pipe work (water or gas) to obtain a continuity reading to check whether they were extraneous or not in their own right. Or did I dream that bit as I was a sleep? My point is that it is fairly difficult to see whether one service is extraneous in its own right or is picking up a connection to earth via another service, water from gas or vice versa, I think their point was it would be easier to bond both if this situation arose irrespective of the plastic feed from one service.
 

Reply to Bonding to gas and 544.1.2 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
403
evening everyone . Quick question here I’ve recently took over a job that a friend of mine first fixed it’s a 3 bed semi house rewire. I don’t...
Replies
10
Views
1K
Hi, went to have a look at a job today, customer has had gas supply company out (for another issue) and they have commented that the protective...
Replies
1
Views
2K
We had our gas disconnected last week and the meter removed. We need to start removing the redundant gas pipes in inside the property. There is...
Replies
6
Views
2K
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock