    Afternoon,

    I've just been to a new build finishing off some lighting and found a fault in the 3c&e between the landing and hallway. No continuity on 1 core.

    It's going to cause a lot of damage to replace the cable. The other 2 cores & CPC are good, IR tests fine.

    Is there anything out there wireless, everything I have seen looks to still need the 3 cores between switches.

    Suggestions welcome!!
     
  2. buzzlightyear
    Offline

    buzzlightyear Electrician's Arms

    Location:
    star command
    if so, than the cable to the hallway to of the stairs needs replacing.
    then is down to plasters to repair the damage .
     
  3. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    How do you know it was the plasterer's fault in the first place, Buzz highly likely but is there, be any proof.
     
  4. buzzlightyear
    Offline

    buzzlightyear Electrician's Arms

    Location:
    star command
    what the betting pete. no capping on the cable .plasters nicked with the blade.
     
  5. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Like I said probably right.
     
  6. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    If it's new build there is no plaster , they board the walls and tape the joints then sand down.
    No plastering involved
     
  7. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    How old is the property? is it still under warranty?
     
  8. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    He said new build didn't he?
     
    • Like Like x 1
  9. buzzlightyear
    Offline

    buzzlightyear Electrician's Arms

    Location:
    star command
    yeah right .who that bob the builder.
     
    • Funny Funny x 1
  10. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Yes, so? all I asked was how old, and is it still under warranty fair question I think and why so fractious with your post?
     
  11. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    Not being fractious, I thought you missed the new build part of the post the op posted.
    Chill out yeah?
     
    • Like Like x 1
  12. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    I work on them from time to time buzz, the major house builders.
    Not a plasterer in sight
     
    • Agree Agree x 1
  13. buzzlightyear
    Offline

    buzzlightyear Electrician's Arms

    Location:
    star command
    it ok boys ,it crunchie Friday!
     
    • Like Like x 3
  14. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    I got my Liam Gallagher tickets so all is good :cool:
     
    • Like Like x 1
  15. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    No mate it's bad news Friday as far as I'm concerned.
     
  16. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    You ok pete?
     
  17. buzzlightyear
    Offline

    buzzlightyear Electrician's Arms

    Location:
    star command
    will he be singing when you go a see him .or is he going to walk of the stage after 5mins and telling the fans to f**K off you paid you monies.
     
    • Like Like x 1
  18. buzzlightyear
    Offline

    buzzlightyear Electrician's Arms

    Location:
    star command
    will he be singing when you go a see him .or is he going to walk of the stage after 5mins and telling the fans to f**K off you paid you monies.
     
    • Like Like x 1
  19. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Yes Ian Thanks, calming down a bit now.
     
    • Like Like x 1
  20. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Scolmore do a wireless switch (https://www.scolmore.com/_pdfs/click-smart.pdf). Least I've seen them every time I walk in & out of my wholesaler. I'm sure there's others. Personally I think the fault should be rectified, being a new property and all that.
     
    • Agree Agree x 3
  21. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    It's under warranty then get it sorted properly, no good throwing half arsed repairs to solve the problem, it need doing properly and paid for by the NHBC or whatever they're called these days.
     
  22. Ian1981
    Offline

    Ian1981 Electrician's Arms

    Location:
    North east
    That's the gamble you take mate haha
     
  23. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Those Gallagher Brothers both of em, are another Pet Hate of mine, wrong thread I know, but as I'm in the mood for peeing people who don't deserve it, might as well add that to my messed up Friday rant, and it was all going so well.
     
  24. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Sounds as if the property hasn't even started it's warranty period yet, i.e. not been handed over to a customer. The fault should be found or cable replaced. You might have a nail or screw in the cable?
     
    • Agree Agree x 3
    • Like Like x 1
  25. rossfenwick
    Offline

    rossfenwick EF Member

    Location:
    Essex
    Thanks Midwest It would be a bit bodge I suppose.

    It is a new build timber frame. It has a 50mm service void on the external walls where the cable drops at ground floor, then along a flat roof joist up the wall at first floor to the loft across the landing and down to the switch. I'm a bit ocd about being clear of the tackers screws, maybe there using 4 inch drywall.s

    Looks like the hole saws are coming out Monday, better get some filler!
     
    • Like Like x 1
  26. Andy-1960
    Offline

    Andy-1960 Electrician's Arms

    Location:
    Wolverhampton
  27. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    • Agree Agree x 4
  28. electric al
    Offline

    electric al Regular EF Member

    Location:
    sheffield
    Think someone has an irrational grudge against plasterers - had them found guilty and sentenced before evidence had been put forward :(
     
  29. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    who givesa sh8t who's fault it was my 110V makits recip saw ( a padsaw on steroids) can find the fault within a minute. ( might create a few more as well).
     
    • Funny Funny x 3
  30. Andy-1960
    Offline

    Andy-1960 Electrician's Arms

    Location:
    Wolverhampton
    I agree, but the OP did ask if there was any wireless option.
     
  31. anthonybragg
    Offline

    anthonybragg Electrician's Arms

    Location:
    NORTHAMPTON
    Business Name:
    CHARLTEC ELECTRICAL LTD
    Got to agree wireless is just a easy way out .
     
  32. anthonybragg
    Offline

    anthonybragg Electrician's Arms

    Location:
    NORTHAMPTON
    Business Name:
    CHARLTEC ELECTRICAL LTD
    Which core is it ? ,the favourite that I used to encounter was skirting board nail below the landing light switch (yes in zone) does this cable have a fault to earth ?.
     
  33. jackhammerJIM
    Offline

    jackhammerJIM Regular EF Member

    Location:
    north yorks
    is it wired as a standard 2 way or 1 way to 2 way conversion ?
     
  34. rossfenwick
    Offline

    rossfenwick EF Member

    Location:
    Essex
    It's Brown.

    No IR' s on cpc black and gray are good.

    Opting for the telectrix recipe method. Hopefully less than 4 holes!!
     
  35. rossfenwick
    Offline

    rossfenwick EF Member

    Location:
    Essex
    Hi Jackhamer, not sure what you mean by conversion.

    Its a 3c&e from first floor sw to ground floor sw. The 2c&e L & Sw L are from the ceiling rose to first floor sw.
     
  36. jackhammerJIM
    Offline

    jackhammerJIM Regular EF Member

    Location:
    north yorks
    that is wired 1 way to 2 way conversion method . would it be easier to convert it to standard 2 way ?
     
  37. ED17
    Offline

    ED17 Electrician's Arms

    Location:
    North West
    True, might have been a plumber!
     
    • Funny Funny x 1
  38. electric al
    Offline

    electric al Regular EF Member

    Location:
    sheffield
    Maybe his missus asked a plasterer round to fill a hole in the bedroom whilst he was out tampering with a length of conduit or something :)
     
  39. Leesparkykent
    Offline

    Leesparkykent You Rock Gmes Staff Member Trusted Advisor

    Location:
    Kent
    Is the switch fed?
     
  40. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    You need to read previous posts aka # 20.
     
  41. jackhammerJIM
    Offline

    jackhammerJIM Regular EF Member

    Location:
    north yorks
    No its dieting :tearsofjoy:
     
    • Funny Funny x 4
  42. UNG
    Offline

    UNG Trusted Advisor

    Location:
    Nr Wigan, Lancs
    How long has this been the "conversion method"
    Was actually taught that as one of the many standard methods to wire a 2 way circuit 40 years ago
     
  43. jackhammerJIM
    Offline

    jackhammerJIM Regular EF Member

    Location:
    north yorks
    It was taught to me as the conversion and standard 17 years ago
     
  44. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    it's been a standard method of 2 way switching for as long as i can remember 3 core/E being available ( and it was in those beautiful red/yellow/blue colours, instead of Yuk, Puke and Fart).
     
    • Like Like x 3
    • Creative Creative x 1
  45. electric al
    Offline

    electric al Regular EF Member

    Location:
    sheffield
    Be nice to get those colors back now we're brexiting - harmonisation FFS
     
    • Agree Agree x 3
    • Optimistic Optimistic x 1