Discuss BS7671:2018 Proposed Changes in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Are there any statistics regarding the failing of PEN conductors and their occurances?
There surely are monitoring systems available to DNOs for these occurances leading to rapid responses.
I thought that TNCS was the future but if wrought with SO MUCH DANGER and the possible need for earth rod back up at every install, it strikes me as not that advanced!
My initial thought is that if this is felt necessary as a requirement for safety due to the nature of the incoming supply, should this not be introduced into ESCQR and not have the onus for this safety measure put upon the end user ?
Increased csa of main bonding is a requirement for safety due to the nature of the incoming supply (PME) as is the use of rcds for fault protection (TT), nobody expects the DNOs to foot the bill for it so why should this be any different?
Then why not do away with that possible problem and go back to TN-S?Increased csa of main bonding is a requirement for safety due to the nature of the incoming supply (PME) as is the use of rcds for fault protection (TT), nobody expects the DNOs to foot the bill for it so why should this be any different?
BBC1 BBC2 ITV and C4 if you were lucky Apprenticeships, Plastic CUs and on and on and on. Glad I'm out to grass, or out to Red Vino, never did like grass, gives me Hay Fever, as well as a hangover. Tried that Mid Eartern stuff once Gaaat I think it was bit like a Privet hedge.sod it. i'm going back to the 16th. RCDs only where sensibly required, CUs didn't spontaneously combust, no 5wws, shared neutrals save cable, no cat 5 run everywhere, sound in every room created by leaving doors open and turning the volume up. and only 4 channels of garbage on the telly instead of 200 . good old days.
Further to my post on the other thread can anyone find anything about AFDD's and where they will be required, other than they may be fitted!
Then why not do away with that possible problem and go back to TN-S?
Cost is the reason pure and simple.
no risk of raising the earth to mains potential due to open pen conductor and no diverted neutral currents.
Earth can still fail of course.
But remember that the supplier does not have to provide a earth facility.I love how the supply authorities issue becomes the installers problem!
Yes the reason for this edict is the failing of older U/G cables or degrading with ageBut remember that the supplier does not have to provide a earth facility.
but 99% of the time they will unless there's a good reason not toBut remember that the supplier does not have to provide a earth facility.
Will be interesting seeing how many domestic installions get condemned for no earth rods, I noticed that now all lighting circuits in domestic installations will have to be rcd protected which is just belt and braces to make sure rcds are fitted on all circuits in a house .
What happens if you live in a block of flats ? or if your posh apartments
What happens if you live in a block of flats ? or if your posh apartments
Hahahaha can just imagine that. One for each flatWell the sensible people will install earth electrodes connected to the MET of the incoming supply to the building.
The less sensible people will be clipping green and yellow cables down the outside of the building to earth rods.