    first time since amendment 3 came out that I have had to install a TT system

    I need to install site temps on a plot of land ready for new build flats.

    UKPN will be installing a new PME temp supply

    Am I right in thinking I am ok to take my tails through a nylon Wiska tail gland- through a amendment 3 board using a clamp. with a 100ma timed delay main switch.

    then 30ma RCBO any of the circuits out of here that need them. think they are getting site cabins with pre wired boards in them anyway.

    Cheers
     
  2. Risteard
    Offline

    Risteard Respected Member

    Location:
    Derry, Ireland
    Business Name:
    Walsh Electrical Services
    Why not an Amendment 0 to the 18th Edition DB?
     
    • Agree Agree x 1
    • Funny Funny x 1
  3. chris gray
    Offline

    chris gray Electrician's Arms

    Are the sub mains in swa? The site cabins will probably be 30mA rcd main switch is all.
     
  4. J.C.E
    Offline

    J.C.E Electrician's Arms

    Location:
    Earth
    knew someone would say that ;)
    well the in question subject is relating to the main part of amendment 3
     
  5. J.C.E
    Offline

    J.C.E Electrician's Arms

    Location:
    Earth
    the subs will likely be SWA yes and yes the cabins will propably has boards in them so 30ma protected there.

    but need the 100ma upfront as will be a TT for a construction site

    but my query is more re tail entry into a metal board on TT.
    is just using a plastic gland and a tail clamp satisfactory
     
  6. spinlondon
    Offline

    spinlondon Forum Mentor

    Location:
    Harlow Essex
    Get one of the Whiska glands for the size of tails you are using.
     
    • Like Like x 1
  7. Leesparkykent
    Offline

    Leesparkykent Super Moderator Staff Member Super Moderator

    Location:
    Kent
    It’s not a dwelling so use a plastic board.
     
    • Like Like x 3
    • Agree Agree x 3
    • Winner Winner x 1
  8. cliffed
    Offline

    cliffed Regular EF Member

    Location:
    Lancs
    Really
     
  9. Leesparkykent
    Offline

    Leesparkykent Super Moderator Staff Member Super Moderator

    Location:
    Kent
    Really what?
     
    • Like Like x 4
  10. cliffed
    Offline

    cliffed Regular EF Member

    Location:
    Lancs
    Obviously joking,why would you even think of installing a plastic DB,that’s really so old fashioned.
     
    • Funny Funny x 1
  11. wirepuller
    Offline

    wirepuller Forum Mentor

    Location:
    south uk
    I'm putting in a plastic board next week.
     
    • Like Like x 1
  12. anthonybragg
    Offline

    anthonybragg Electrician's Arms

    Location:
    NORTHAMPTON
    Business Name:
    CHARLTEC ELECTRICAL LTD
    Would you not consider a 100mA time delayed RCD?
    EDIT----Apologies in post one you said T/Delayed it had gone from the next post but assume still being so. Metal or plastic preferably a IP one.
     
    Last edited: Jan 9, 2019
  13. Leesparkykent
    Offline

    Leesparkykent Super Moderator Staff Member Super Moderator

    Location:
    Kent
    No def not a joke.....
     
  14. Leesparkykent
    Offline

    Leesparkykent Super Moderator Staff Member Super Moderator

    Location:
    Kent
    2626A2AE-A17B-487C-AB4B-4EDAA92F8B2A.jpeg Something like this is what I’d usually use for a temp supply on a building site
     
    • Like Like x 2
    • Winner Winner x 2
  15. Risteard
    Offline

    Risteard Respected Member

    Location:
    Derry, Ireland
    Business Name:
    Walsh Electrical Services
    That looks like a Vector enclosure. Use them quite a bit for IP-rated stuff (with Gamma enclosures for insulating enclosures indoors not requiring IP rating).
     