B

Boberto

Is the most common cause of this problem a loose connection? I came across a burnt out neutral wire on a 100A DP main switch earlier. It was hard to tell if it was loose as it was charred and burnt so bad I couldnt tell! The burnt wire was the 16mm incoming neutral.

The establishment is a fast food take away. There are a number of 100A DP switches supplying flats above, the basement and the main shop area. The isolator where the problem occured was supplying the shop which is in use 7 days a week 10-12 hours aday. Current = 25A approx when checked with clamp meter however when the deep fat fryers kick in the current drawn was showing around 60A. That is the only appliance pulling current of any size. The rest of the shop consumes of grid lighting and a couple of ring finals which supply juice to chest freezers, the till, fly exocutor etc.

From the isolators 16mm tails supply the consumer units located in basement, flats and shop (10-15m distance approx). The main fuse is 80A and the 16mm tails are installed in MT4 trunking to the sub mains with main earth.

Am I missing something? Could this merely be a loose cable connection or is there a chance this is a loading issue. I was under the impression 16mm tails fine protected by a 80A main fuse providind the tails are clipped direct of installed in correct spacing factor trunking?

Advice....?
 
Just to mention the burnt parts were the incoming neutral terminal on the main switch and about 4 to 5 inches of the incoming 16mm neutral. All other parts of the cable are fine including the outgoing 16mm neutral. I wanted a 2nd opinion because with the fryer switching itself on when the temperature of the oil in it drops the current drawn to the shop increases to 60A. Just wanted to make sure that the size tails were sufficient on a 80A main fuse. As I said, loose connection is always my first evaluation on these sort of faults too.

Thanks.
 
The only other cause, is bad contact on the DP switch, but then i would of expected to see extensive heat damage to the housing of the switch. As Marvo states ....By far the most common cause for these types of failures is a loose connection at the cable terminal point...
 
As to the remedial work for it, replace the switch as well as remaking the cable. You may have to cut back beyond the burnt area of insulation, heat softens copper so will not make a good connection. Copper that has been heated has a darker colour when you cut it, so you should be able to see how far back the go. If needs be you’ll have to put in a through crimp and then sleeve it. Likewise any springs in the switch will be weakened by heat.
 
Your in the best situation to do a good repair then.
You don’t have Mrs. Brown from flat four breathing down your neck.
BUT there again you’ve got to make your own tea…. Bugger, there’s a down side to everything!

Going back to what I said, anything that shows sign of heat damage, sort it now while you can do it in your own sweet time.
 

Reply to Burnt neutral wire on 100A main switch... in the Australia area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
790
I've been carrying out quite a few domestic extension first fixes recently which involves providing a power supply installed from the properties...
Replies
7
Views
2K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
879
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock