Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Discuss C1 for no SWA cable underground but is in high tuff in the Periodic Inspection Reporting & Certification area at ElectrciansForums.co.uk.

Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. Mr AB
    Offline

    Mr AB EF Member

    Location:
    West Sussex
    hi just a quick question, I’ve been asked to re-test a block of flats which has just had an EICR done. Was and old board etc, had 2 new RCD boards fitted so no issues there! They have now quoted a lot of money to replace a cable which runs under ground (no idea how) in high tuff cable. This has been given a C1 and quote is to dig up the road etc to replace. I can see the previous issue when there was no RCD protection but now there is so I personally don’t see this as a C1 now an RCD for this particular circuit has been fitted, any ideas on this going forward?
     
  2. Leesparkykent
    Offline

    Leesparkykent Super Moderator Staff Member Super Moderator

    Location:
    Kent
    FI would probably be more appropriate but would still end up with the same result being an unsatisfactory report. If the high tuff is installed in a duct that is to BS EN 61386-24 (twin walled duct) then it’s not a problem. To be honest it could of been recorded as an agreed limitation/operational limitation as not to dig up the car park to establish the installation method of the circuit in question and then it would of been satisfactory. You wouldn’t dig it up to see if there was warning marker tape would you :D
     
    • Like Like x 2
    • Agree Agree x 1
  3. Mr AB
    Offline

    Mr AB EF Member

    Location:
    West Sussex
    Totally agree, the management company are obviously quite keen on not wanting to be paying over 2k for this to be corrected, it goes under the main raod in to the block so you would think some kind of conduit/duct has been used for this but it’s just a guess! Not really sure what to go back to them with as it’s not an ideal situation!
     
  4. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    immediate danger? yes or no? ... C1

    potential danger? yes or no? C2

    improvement recommended? C3.

    you can only code as above. it may not be ideal, but if it's safe, then you can't give it an unsatisfactory code.
     
    • Like Like x 1
  5. Murdoch
    Offline

    Murdoch Regular EF Member

    Location:
    Woking
    Definitely not C1

    Any signs of damage - if so maybe C2

    Otherwise it’s a C3 for me .....

    What code number has the inspector given to back up his C1?
     
    • Agree Agree x 1
  6. Flanders
    Offline

    Flanders Regular EF Member

    Location:
    Tamworth
    Well it is not a code 1. If its going through an area with no soft dig then may be not a code 2 expecially as it covered by an rcd, What you nead to ask yourself is would you put you name to an eicr saying its safe , if yes then tell the customer you will carry out an eicr on this part of the installation and code it as you think , if you could get hold of the installation cert it may help you .
     
  7. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    when you consider that a lot of supplies come in in unarmoured concentric, no ducting,
     
    • Like Like x 1
  8. Strima
    Offline

    Strima Electrician's Arms

    Location:
    St Neots
    If the cable is in suitable duct that provides mechanical protection in accordance with manufacturers instructions then no code, if it's buried direct with no mechanical protection then I would more than likely C2 it.
     
    • Agree Agree x 1
  9. Leesparkykent
    Offline

    Leesparkykent Super Moderator Staff Member Super Moderator

    Location:
    Kent
    Get a labourer to expose the duct...if there is one.
     
  10. Flanders
    Offline

    Flanders Regular EF Member

    Location:
    Tamworth
    Good point , do they do have their own rules
     
  11. Mr AB
    Offline

    Mr AB EF Member

    Location:
    West Sussex
    Thanks for all the replies, I am basically going to be going along the lines of recommendation that the cable is replaced but currently no immediate danger but going forward testing the circuit every year if any deterioration happens then we replace! At least they know in the coming years this could happen and be ready for it!
     
  12. Murdoch
    Offline

    Murdoch Regular EF Member

    Location:
    Woking
    Hold on .... was it you that gave the C1?
     
    • Agree Agree x 1
  13. Leesparkykent
    Offline

    Leesparkykent Super Moderator Staff Member Super Moderator

    Location:
    Kent
    I don’t really see the point in more regular testing of the circuit. It’s either compliant or not and surely that’s what the customer wants to know?
     
  14. Mr AB
    Offline

    Mr AB EF Member

    Location:
    West Sussex
    No was not me who gave a C1, they had such a list even after having works done and the new circuit boards, I got a call for a 2nd opinion. They have even given a C2 for lights and smoke alarms on the same circuit
     
    • Like Like x 1
  15. Murdoch
    Offline

    Murdoch Regular EF Member

    Location:
    Woking
    And this alone calls into question the reliability and knowledge of the inspector

    Again, did they quote a reg number to back up this C2?
     
    • Agree Agree x 5
Loading...
Similar Threads - cable underground high Forum Date
Consumer Unit replacement cables not long enough. Electrical Forum Tuesday at 6:54 PM
Finding out length of cable through measuring resistance. The Electricians Arms Feb 14, 2019

Share This Page

Users found this page by searching for:

  1. tuff flex wiring

Electricians Directory Post a Domestic Job Post a Commercial Job