Is the rest of the lighting circuit earthed? in other words has some Dilbert just run a 2 core cable to the units off of the existing circuit ?

No, the entire upstairs is unearthed, however, there was a test in 1998 and the tester recorded a Zs for the upstairs lighting, so three possibilities.
1) The circuit has lost it’s earth.
2) The result recorded was a mistake.
3) There are 3 cables in the MCB and the old Zs recorded is surprisingly low for the length of the cable I was trying to measure, so the Zs test results may be at a point on one of the other cables that is earthed.

NOTE: The florescent fittings are the only class 1 fitting on the upstairs, no metal switches or lights.
It is twin and earth to the pendants I can get into and into the florescent fittings but floating earth at the pendants and florescent fittings.
I will be doing some investigation to see if the three cables are Twin and earth from the consumer unit and if it is, finding the break in the cable somewhere.
I will also have to break into one of the 1960’s pendants in the old part of the building to replace it, and then I will be able to confirm if the cable used originally is T&E or just 2 core.
 
So you are saying there is a cpc present but it has no continuity, or there is no cpc present.
 
So you are saying there is a cpc present but it has no continuity, or there is no cpc present.
Yes, I was not thinking straight. There is a CPC in the upstairs 1980’s extension but no earth continuity. I had assumed that as there were no class 1 fittings upstairs (Until I discovered the Florescent fittings) that the 80’s extension wiring had extended the non earthed old lighting circuit, but it should have been earthed when it was built, so I will need to be investigating and re-instating the earth to the upstairs lighting circuit and confirming the old part of the building is earthed.
 
Yes, I was not thinking straight. There is a CPC in the upstairs 1980’s extension but no earth continuity. I had assumed that as there were no class 1 fittings upstairs (Until I discovered the Florescent fittings) that the 80’s extension wiring had extended the non earthed old lighting circuit, but it should have been earthed when it was built, so I will need to be investigating and re-instating the earth to the upstairs lighting circuit and confirming the old part of the building is earthed.
Probably find that some Dilbert doing the 2nd fix cut all the cpcs off because "they aren't needed"
 

Reply to C2 or C3 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've tried to research and form a plan without asking on here, but I'm just going around in circles. Just completed an EICR. The wiring ranges...
Replies
15
Views
2K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
692
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
500
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
So I'm getting various responses to this depending on how things are interpreted. Here's a scenario: Assume property is a tenanted property...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock