    Hi wondering if anyone has any advice on what type of cable would be best.

    I need to run a 600amp 3 phase feed with neutral using single core with power lock connectors for just under 50meter across the open floor with short sections in cable ramp, from this it will be broken down into 3x 125amp 3 phase connectors each taking just under 100amp per phase.
    This will feed some 3 phase equipment and also break down into several single phase supplies.
    For shorter runs of this I have used H07RNF at 120mm, but wondering on sizing for this length run and if there are alternatives to H07RNF that would give us the same current capacity still be flexible enough to move and keep with in our voltage drop.
    Thank for any help.
     
  2. Ian1981
    Offline

    Ian1981 Forum Mentor

    Location:
    North east
    Tri rated cables
     
  3. buzzlightyear
    Offline

    buzzlightyear please let me back in to the prison cell.

    Location:
    star command
  4. buzzlightyear
    Offline

    buzzlightyear please let me back in to the prison cell.

    Location:
    star command
  5. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Staff Member Moderator

    Location:
    Northamptonshire
    The OP has asked a question there is no need to drill him over his qualifications. The offending and now not relevant posts are gone.
     
  6. Johnthefixer
    Offline

    Johnthefixer EF Member

    Location:
    Gloucester
    No offence taken quite happy to be asked. my questions is more of a general enquiry, in case I have missed a type of cable that could be use. Your link to the cleveland trirated is for panel wiring cable is this not really suitable for laying on the ground in exposed areas?
     
  7. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Staff Member Moderator

    Location:
    Northamptonshire
    Glad you understand but these questions can quickly throw a thread off course and at times stop new members pursuing the thread.
    Yes tri rated conductors would require additional protection.
     
  8. Johnthefixer
    Offline

    Johnthefixer EF Member

    Location:
    Gloucester
    so H07 rnf is the only option?
     
  9. Rob
    Offline

    Rob Respected Member

    Location:
    North west
    Tri rated isn't suitable unless the entire run is mechanically protected in trunking or similar.
     
  10. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Staff Member Moderator

    Location:
    Northamptonshire
    Your options are very limited and HO7RNF offers the best option as it has good mechanical properties.
     
  11. Johnthefixer
    Offline

    Johnthefixer EF Member

    Location:
    Gloucester
    So sizing H07 RN-F for 600amp per phase at 50m laying on the ground.
     
  12. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Staff Member Moderator

    Location:
    Northamptonshire
    You need to do some calculations taking volt drop into consideration but it will be 500 to 630mm. I would suggest contacting Cleveland or Eland cables for an accurate sizing.
     
  13. TonyMitchell
    Offline

    TonyMitchell Electrician's Arms

    Location:
    Berkshire, UK
    50m is 340kg per single = 1.7t for the five!
     
  14. essex
    Offline

    essex Forum Mentor

    Location:
    Wiltshire
    Have you considered dual feeder?
     
  15. Johnthefixer
    Offline

    Johnthefixer EF Member

    Location:
    Gloucester
    whats dual feeder?
     
Loading...
Similar Threads - cable selection 600amp Forum Date
Domestic Induction hob butyl cable size DIY Electrical Forum Yesterday at 7:38 PM
Commando Socket Cable Size Commercial Electrical Talk Yesterday at 4:26 PM

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job