Noted today an interesting comment on page 43 of christopher kitchers Practical guide to inspection, testing and certification of Electrical Installations ( a great book )

Under Shower curcuits he states:
For this type of circuit it is possible to have a cable which has a current rating of less than the rating of the protective device. This is because we do not have to provide overload protection to circuits which cannot overload.

Is this accuate and safe? Isn't it possible for a shower heater element fail in a way that draws extra current?
 
It's almost impossible for a sheathed heating element to short in such a way that the resistance between L & N is reduced. Element failures usually involve a short to the metallic sheath which will trip an RCD and/or blow itself to pieces due to the heat / arcing concentrated at the fault. Other faults would be hard shorts in the internal wiring or controls, which require only short circuit protection, not overload. If, somehow, a fault occurred to earth near the neutral end of the element on a non-RCD-protected circuit, the load could theoretically increase, but if it were sufficient increase to risk cable damage the thermal fuse or limit stat would probably open anyway.
 
Good points. Yes most shower or immersion faults I've fixed have been shorts to the metal sheath. Normally due to limescale build up causing local overheating.
As every water heating device over 15ltr capacity needs to be on its own circuit I can't see why it would have a protective device over the cable rating?
When could that occur?
 
Thanks Wilco. Interesting thread and 20mins of my life used up:)
 

Reply to Cable size less than protective device rating in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a 40amp RCD downstream of a 50a MCB (10mm csa cable) should the MCB be lowered to protect the RCD from overload? If so why does this not...
Replies
4
Views
766
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
Just thought I'd share this quick sobering story that happened to me a couple of weekends ago.... Overhead 230v lighting festoon, LED golf ball...
Replies
5
Views
732
Hi, I have a question regarding the cable size to a 415v 125A socket. For the design current is it normal to use the protective device rating of...
Replies
14
Views
2K
This from a while ago but reading about everyone elses problems tonight made me remember this one. The original job was the lights in a recent...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock