so ypu came out the distribution boards in to a lv switch panel to 125a isolator have you got a diagram i am very interested in massive cables and industrial
 
Is the 50 kW figure total power or power for each phase? Have they said if there is a power factor involved and whether it is connected in star or delta?
 
50kw power intotal: No power factor as i know of. No i do not know if its delta or star! If in delta you would not need to carry a nuetrul to the isolator would you?
 
50kw power intotal: No power factor as i know of. No i do not know if its delta or star! If in delta you would not need to carry a nuetrul to the isolator would you?

correct,no neutral if in delta.

power=√3 x Vl x Il

so rearrange to get Il which will be your design current Ib
 
does that mean even though the DB has a N you still do not need to bring a N to the machine??

and say you have 1x 3 phase (100A per phase) CU with say umm 12 ways and you want to run this 50kw load from this supply..

how does switch panel work and does it run of the DB eg

DB - switch panel - from SP to the mccb then from there to the isolator?
 
No practical expert by any means but if it is a motor connected in delta there will be no neutral - it will be a balanced load with no resultant neutral current.

Forgot to say before that your power per phase willbe a 1/3 of the total power, still use the √3 though.

reckon your line current in each phase is 24A if ihave used this rubbish windows calculator properly.

edit Il (line current) will be 72A as does not need dividing by 3 - reason you are dealing withtotal power, line currents and line voltages, not Ip and Vp and power per phase
 
Last edited by a moderator:
so if each phase is carrying 24A then a 70mm cable will not be needed. i have taped in a cable calculot on the net and it come up with 16mm. im very confused about what to put and how i got 16mm and some one came up with 70mm??

so what cable will i need?
 
:)Have a look at page 123 temp at 30C has no affect so can be disregard it in this case (table 6A) the other circuit derates it though-look at top line of table 6C (p126) . You will need to divide your current by 0.8

tricky question this one :)
 
some1 help bugsy how did you work it out and what amps per phase do u get? im confused about the incoming tails say they are in 25mm per phase in to the board would u then come from the DB to the switch panel if so what cable size would u use then? can u some how find a diagram of it please mate
 

Reply to cable sizes in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Happy New Year all. Quick question regarding cable sizing. I have a 25m run from DB to car charging unit. The 25m run will mean approx 8m is run...
Replies
5
Views
646
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
678
I am an enthusiastic retired engineer rebuilding a barn in France from scratch and am having problems sizing my incoming electrical cables. I have...
Replies
6
Views
2K
Thinking of getting a Runpotec XB300 cable dispenser, as my yellow framed tripod thing is unsatisfactory for all the usual reasons. You can...
Replies
8
Views
573
Hi All I would appreciate some help with a few questions here regarding cables sizing, I'm using the latest 18th edition, amendment 2. Q1...
Replies
0
Views
885

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock