Hi again,
2.5 TE cable installed within fully insulated partition walls which i would of thought is now pretty mush standard now on new builds / refurbishments. According to OSG guide table F6 page 150 Ref method 103. 2.5mm cable down rated to 13.5 amps! Radial for imm/htr would be 16 amp breaker, therefore wrong, cable would have to have to be 4mm. Ring circuit double up. would on give 27amps, normally 32 amp breaker but in this case Breaker down to 20amp. Am i reading the tables correctly/
 
if cable is in contact with one side of the partition, then it's method 102.
 
You're correct if you want to stick the cable down the centre of the insulation. As tel says, should be in contact with one side of the partition. If not possible, then you could always go with ref method A.
 

Reply to Cables installed in insulated partition walls in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm currently refurbishing a room and in the process adding some internal wall insulation. The wall has been stripped and my electrician has...
Replies
5
Views
2K
Hey all, Ive been in and out of a huge house rewiring as the renovate it for a year of so. Every is thing done and dusted except the downstairs...
Replies
3
Views
1K
Hi My 4 bed 2 storey house was extended 2 years ago and completely re-wired, but I am having to upgrade the insulation and board out the loft...
Replies
0
Views
1K
Hi We recently had an 7kW EV charger installed. Due to the consumer unit being situation within the kitchen of our bungalow, the cable needed to...
Replies
10
Views
4K
Hi everyone. I need a little advice please. Several months ago I first fixed and second fixed a timber frame loft conversion ( open plan living...
Replies
18
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock