I have to calculate the total consumption for each of the circuits and state the final maximum demand current.

downstairs :2 fittings with 5x 12w lamps,1 fitting with 5 x 12w
1 fitting with 10 x 12w,1 fitting with 1 x 60w,1 fitting with 7 x 20w
2 fitting with 3 x 20w,1 fitting with 4 x 30w and 2 fitting with 1 x 20w,cooker 5.1kw

upstairs: 1 fitting with 5 x 12w,3 fitting with 1 x 20w,1 fitting with 1 x 60w, 1 fitting with 1 x 60w, 1 fitting with 1 x 60w, 1 fitting with 5 x 12w and 4 fitting with 1 x 20w. shower 9.8kw

Also , Upstairs: 10 sockets and Downstairs: 13 sockets and 4 fuses.

So far I've got:

Downstairs:

780w x1.8 / 240 = 5.85a

Kitchen cooker power consumption: 5100 w
x 1.8 / 240 = 38.25a
10a + 11.48a + 5a= 26.48
Upstairs
440w x 1.8 / 240 = 3.30a
Bathroom shower power consumption:
9800w x 1.8 / 240 = 73.5a
Upstairs: 10 sockets
100%X + 40%(Y+Z)

Downstairs: 13 sockets and 4 fuses
100%X + 40%(Y+Z)

13a13 - 60% = 5.2 = 13+5.2 = 18.2 seems wrong! ?
X is the full load current of the largest appliance or circuit
Y is the full load current of the second largest appliance or circuit
Z is the full load current of the remaining appliances or circuits
 
Re: calculating total consumption for each of the circuits and final maximum demand c

Welcome to the forum. Is this a college homework question?
 
Re: calculating total consumption for each of the circuits and final maximum demand c

Look up diversity in either OSG or BS 7671
 
Re: calculating total consumption for each of the circuits and final maximum demand c

What's the x1.8 for? Thought that 1.8 factor was only applied to discharge lighting?
 
Re: calculating total consumption for each of the circuits and final maximum demand c

he's other question is pretty good too!
 

Reply to calculating total consumption for each of the circuits and final maximum demand curre in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Pretty new here, so not sure if this question goes into this thread I am not an electrician; however, I plan to integrate IOT devices and...
Replies
8
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
Replies
54
Views
6K
A couple of questions for you. The electrician that rewired our house ran a 10mm2 SWA to our outbuilding. The total length of the cable is about...
Replies
17
Views
4K
Greetings everyone. My first post here, having read a similar thread, I understand that following the manufacturers guidance is all important...
Replies
10
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock